On Friday, November 1, 2019 at 5:32:14 AM UTC-4, Piotr Wyderski wrote:
A main breaker obviously does both. You can't exceed the limit of
the fuse, that certainly "throttles" the total capacity of the service.
It also only protects the wires against an overload past the breaker.
It doesn't protect the wires between the transformer and breaker.
If something comes in contact with them, the breaker does nothing.
Which is different than a breaker protecting branch circuits, where
the breaker protects the wiring from the breaker to the loads.
No, we use wire. Not unusual to see 100A subpanels, for example,
wired to the main panel. And that's just the peak capacity.
Actual usage is something totally different. The bill here is
typical ~600kwh for a month. That works out to about 7a continuous.
The wire losses depend on the current. If we take an average wire
run of 50 ft, use 14g which is the smallest branch circuit gauge
allowed, you have a whopping .25 ohms resistance. Using a 7a
current, that works out to 12 watts lost, 840 watts delivered
to the load. That's a loss of just 1.4%. If we doubled the
voltage, the loss would be 0.7%, not what I'd call significant.
My bill for that monthly power is about $75. So, I'd save 52 cents
a month. Doesn't get me too excited....
If we were to start from scratch, I see
compelling advantages to going with 240V as the standard for all
loads, eg an electric kettle could heat twice as fast. I see
some small advantages, eg the 50 cents above, but I sure
don't see a compelling advantage to 3 phase for homes.
In other words, you have no explanation.
The only kitchen equipment in a house that I'm aware of that needs a
lot of power are cooktops and ovens and I wouldn't call those
"enormous". We run those off 240V single phase just fine. Typically
a 30A or 40A circuit. Which also works fine for AC equipment,
heat pumps, etc.
Rick C wrote:
What is stupid about that? It is to protect the line coming into the home.
Stupid is that they are rated WAY below the capacity of the line and
their value reflects the maximal allocated power budget, as per ones
contract. E.g. a typical older flat has 20A fuse, because the contract
specifies 4.5kW power budget. You can get at most 32A on a single phase
and on this very same line -- this is entirely a contractual update. If
you need more, you need to upgrade to a three-phase system. Then you get
3x20A.
The building lines are protected separately.
In case of houses the limits are higher, usually 3x63A, but I have never
heard of 200A. This rating is typical for buildings.
We do the same here.
No, you protect the lines, not throttle the consumption level. This is OK.
A main breaker obviously does both. You can't exceed the limit of
the fuse, that certainly "throttles" the total capacity of the service.
It also only protects the wires against an overload past the breaker.
It doesn't protect the wires between the transformer and breaker.
If something comes in contact with them, the breaker does nothing.
Which is different than a breaker protecting branch circuits, where
the breaker protects the wiring from the breaker to the loads.
Yes, we save on lighting expenses that way. ;-)
But come on, you claimed 90A wiring capability elsewhere in the thread.
Do you use busbars for that? 90A is 8W waste power per milliohm -- creepy.
No, we use wire. Not unusual to see 100A subpanels, for example,
wired to the main panel. And that's just the peak capacity.
Actual usage is something totally different. The bill here is
typical ~600kwh for a month. That works out to about 7a continuous.
The wire losses depend on the current. If we take an average wire
run of 50 ft, use 14g which is the smallest branch circuit gauge
allowed, you have a whopping .25 ohms resistance. Using a 7a
current, that works out to 12 watts lost, 840 watts delivered
to the load. That's a loss of just 1.4%. If we doubled the
voltage, the loss would be 0.7%, not what I'd call significant.
My bill for that monthly power is about $75. So, I'd save 52 cents
a month. Doesn't get me too excited....
If we were to start from scratch, I see
compelling advantages to going with 240V as the standard for all
loads, eg an electric kettle could heat twice as fast. I see
some small advantages, eg the 50 cents above, but I sure
don't see a compelling advantage to 3 phase for homes.
You still haven't explained any reason why you would need three phase power in the home.
Nothing needs to be explained, because this is whay you are given
without asking. You don't need to explain the need for a water pipe as well.
In other words, you have no explanation.
What do you need with three phase in the home that you can't supply with 240 volts?
The kitchen equipment can use enormous amount of power. Waer heaters
even more.
The only kitchen equipment in a house that I'm aware of that needs a
lot of power are cooktops and ovens and I wouldn't call those
"enormous". We run those off 240V single phase just fine. Typically
a 30A or 40A circuit. Which also works fine for AC equipment,
heat pumps, etc.