On Sun, 06 Nov 2022 22:30:36 GMT, Cindy Hamilton
<hamilton@invalid.com> wrote:
Was this in the US with \"pigs\" in the poles ?
To my understanding the medium voltage feed is three phase open wire
in delta configuration (no neutral). The \"pig\" is a single phase
transformer with the primary connected between two phase wires in the
medium voltage feed. The third phase wire is not used by this
transformer, but most likely in the next pig. The secondary is center
tapped with 2 x 120 V. The cent re tap is connected to neutral and
ground.
Are you sure that the wire between pig secondary CT to your house
neutral was broken ?
Your description sounds more like a phase wire of the open wire medium
voltage feed was broken. If your pig did not use this phase, you
would not observe anything strange on your low voltage side, you would
have well balanced 2 x 120 V.
Note that the third wire on the medium voltage side is not neutral,
but the third phase connector.
<hamilton@invalid.com> wrote:
On 2022-11-06, Ralph Mowery <rmowery42@charter.net> wrote:
In article <op.1u73hbz8mvhs6z@ryzen.home>, CK1@nospam.com says...
Not necessarily. We have a \"guaranteed\" minimum and maximum supply
voltage. Why should a company spend extra designing and installing
protection against supplies (not temporary aberrations) outside them?
Because other things could cause lower voltage, like a wiring fault in the device or the building. Especially in dual voltage countries like the US where you can lose one live.
If the neutral line is lost or a bad connection the line voltage in a
house could have one side to be very low and the other side very high in
the US system.
Funny you should mention that. Our neutral broke in high winds
yesterday. Both remaining legs seem to be well balanced.
Was this in the US with \"pigs\" in the poles ?
To my understanding the medium voltage feed is three phase open wire
in delta configuration (no neutral). The \"pig\" is a single phase
transformer with the primary connected between two phase wires in the
medium voltage feed. The third phase wire is not used by this
transformer, but most likely in the next pig. The secondary is center
tapped with 2 x 120 V. The cent re tap is connected to neutral and
ground.
Are you sure that the wire between pig secondary CT to your house
neutral was broken ?
Your description sounds more like a phase wire of the open wire medium
voltage feed was broken. If your pig did not use this phase, you
would not observe anything strange on your low voltage side, you would
have well balanced 2 x 120 V.
Note that the third wire on the medium voltage side is not neutral,
but the third phase connector.