Why do EVs not use the full 3.12kW from a mains socket?...

C

Commander Kinsey

Guest
In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2.3kW.\"

Why? A UK socket is 13A, or 3.12kW.
 
On Fri, 14 Apr 2023 14:57:15 +0100, Commander Kinsey <CK1@nospam.com> wrote:

In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2.3kW.\"

Why? A UK socket is 13A, or 3.12kW.

ROFL! \"The typical cost of a home charge point is around £800.\"

Er.... £100 2nd hand on Ebay plus a bit of cable to connect it to the fusebox. Not £800.
 
In <op.13d81pc2mvhs6z@ryzen.home> \"Commander Kinsey\" <CK1@nospam.com> writes:

In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2.3kW.\"

Why? A UK socket is 13A, or 3.12kW.

I\'ll play the stright cow here. In the USofA, a \"continous load\"
on a circuit is generall maxed at at _80 percent_ of the rated
wire/circuit carrying capcity.

Reason: heat buildup.

I suspect, with no foundationwhatsever, the UK uses
the same concepts.

--
_____________________________________________________
Knowledge may be power, but communications is the key
dannyb@panix.com
[to foil spammers, my address has been double rot-13 encoded]
 
On Friday, April 14, 2023 at 9:57:25 AM UTC-4, Commander Kinsey wrote:
In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2..3kW.\"

Why? A UK socket is 13A, or 3.12kW.

That\'s about the right, a derating to 80%. The socket may be rated for that current, but the connecting wiring may not be able to handle the temperature rise. It saves the homeowner the cost of a new circuit installation, which for most people equates to hiring an electrician and obtaining a permit.
 
On Fri, 14 Apr 2023 14:57:15 +0100, Birdbrain Macaw (aka \"Commander Kinsey\",
\"James Wilkinson\", \"Steven Wanker\",\"Bruce Farquar\", \"Fred Johnson, etc.),
the pathological resident idiot and attention whore of all the uk ngs,
blathered again:

<FLUSH the subnormal sociopathic trolling attention whore\'s latest
attention-baiting sick bullshit unread again>

--
damduck-egg@yahoo.co.uk about Birdbrain Macaw\'s (now \"Commander Kinsey\" LOL)
trolling:
\"He is a well known attention seeking troll and every reply you
make feeds him.
Starts many threads most of which die quick as on the UK groups anyone
with sense Kill filed him ages ago which is why he now cross posts to
the US groups for a new audience.
This thread was unusual in that it derived and continued without him
to a large extent and his silly questioning is an attempt to get
noticed again.\"
MID: <be195d5jh0hktj054mvfu7ef9ap854mjdb@4ax.com>

--
ItsJoanNotJoann addressing Birdbrain Macaw\'s (now \"Commander Kinsey\" LOL):
\"You\'re an annoying troll and I\'m done with you and your
stupidity.\"
MID: <e39a6a7f-9677-4e78-a866-0590fe5bbc38@googlegroups.com>

--
AndyW addressing Birdbrain:
\"Troll or idiot?...
You have been presented with a viewpoint with information, reasoning,
historical cases, citations and references to back it up and wilfully
ignore all going back to your idea which has no supporting information.\"
MID: <KaToA.263621$g93.262397@fx10.am4>

--
Phil Lee adressing Birdbrain Macaw:
\"You are too stupid to be wasting oxygen.\"
MID: <uv2u4clurscpat3g29l7aksbohsassufe2@4ax.com>

--
Phil Lee describing Birdbrain Macaw:
\"I\'ve never seen such misplaced pride in being a fucking moronic motorist.\"
MID: <j7fb6ct83igfd1g99rmu4gh9vf610ra3jk@4ax.com>

--
Tony944 addressing Birdbrain Macaw:
\"I seen and heard many people but you are on top of list being first class
ass hole jerk. ...You fit under unconditional Idiot and should be put in
mental institution.
MID: <VLCdnYC5HK1Z4S3FnZ2dnUU7-dPNnZ2d@giganews.com>

--
Pelican to Birdbrain Macaw:
\"Ok. I\'m persuaded . You are an idiot.\"
MID: <obru31$nao$3@dont-email.me>

--
DerbyDad03 addressing Birdbrain Macaw (now \"Commander Kinsey\" LOL):
\"Frigging Idiot. Get the hell out of my thread.\"
MID: <4d907253-b3b9-40d4-be4d-b32d453937e0@googlegroups.com>

--
Kerr Mudd-John about Birdbrain Macaw (now \"Commander Kinsey LOL):
\"It\'s like arguing with a demented frog.\"
MID: <op.yy3c02cqmsr2db@dell3100.workgroup>

--
Mr Pounder Esquire about Birdbrain Macaw (now \"Commander Kinsey\" LOL):
\"the piss poor delivery boy with no hot running water, 11 cats and
several parrots living in his hovel.\"
MID: <odqtgc$iug$1@dont-email.me>

--
Rob Morley about Birdbrain:
\"He\'s a perennial idiot\"
MID: <20170519215057.56a1f1d4@Mars>

--
JoeyDee to Birdbrain
\"I apologize for thinking you were a jerk. You\'re just someone with an IQ
lower than your age, and I accept that as a reason for your comments.\"
MID: <0001HW.1EE2D20300E7BECC700004A512CF@news.eternal-september.org>

--
Sam Plusnet about Birdbrain (now \"Commander Kinsey\" LOL):
\"He\'s just desperate to be noticed. Any attention will do, no matter how
negative it may be.\"
MID: <rOmdndd_O7u8iK7EnZ2dnUU78TGdnZ2d@brightview.co.uk>

--
thekmanrocks@gmail.com asking Birdbrain:
\"What, were you dropped on your head as a child?\"
MID: <58ddfad5-d9a5-4031-b91f-1850245a6ed9@googlegroups.com>

--
Christie addressing endlessly driveling Birdbrain Macaw (now \"Commander
Kinsey\" LOL):
\"What are you resurrecting that old post of mine for? It\'s from last
month some time. You\'re like a dog who\'s just dug up an old bone they
hid in the garden until they were ready to have another go at it.\"
MID: <59d8b0db.4113512@news.eternal-september.org>

--
Mr Pounder\'s fitting description of Birdbrain Macaw:
\"You are a well known fool, a tosser, a pillock, a stupid unemployable
sponging failure who will always live alone and will die alone. You will not
be missed.\"
MID: <orree6$on2$1@dont-email.me>

--
Richard to pathetic wanker Hucker:
\"You haven\'t bred?
Only useful thing you\'ve done in your pathetic existence.\"
MID: <orvctf$l5m$1@gioia.aioe.org>

--
clare@snyder.on.ca about Birdbrain (now \"Commander Kinsey\" LOL):
\"\"not the sharpest knife in the drawer\"\'s parents sure made a serious
mistake having him born alive -- A total waste of oxygen, food, space,
and bandwidth.\"
MID: <s5e9uclqpnabtehehg3d792tmll73se0g8@4ax.com>

--
Mr Pounder exposing sociopathic Birdbrain:
\"You will always be a lonely sociopath living in a shithole with no hot
running water with loads of stinking cats and a few parrots.\"
MID: <os5m1i$8m1$1@dont-email.me>

--
francis about Birdbrain (now \"Commander Kinsey\" LOL):
\"He seems to have a reputation as someone of limited intelligence\"
MID: <cf06cdd9-8bb8-469c-800a-0dfa4c2f9ffa@googlegroups.com>

--
Peter Moylan about Birdbrain (now \"Commander Kinsey\" LOL):
\"If people like JWS didn\'t exist, we would have to find some other way to
explain the concept of \"invincible ignorance\".\"
MID: <otofc8$tbg$2@dont-email.me>

--
Lewis about nym-shifting Birdbrain:
\"Typical narcissist troll, thinks his shit is so grand he has the right to
try to force it on everyone
MID: <slrnq16c27.1h4g.g.kreme@jaka.local>
 
On Fri, 14 Apr 2023 14:08:47 -0000 (UTC), danny burstein, another mentally
handicapped troll-feeding senile SHITHEAD, blathered:


I suspect, with no foundationwhatsever, the UK uses
the same concepts.

I suspect, the trolling gay sociopathic wanker, just successfully baited
another one the many senile assholes infesting these ngs. <BG>

--
More from Birdbrain\'s (now \"Commander Kinsey\" LOL) sociopathic world:
\"Why do people get upset about getting punched on the nose? It\'s only as bad
as falling off your bike.\"
MID: <op.ymrl1ke48hfnum@red.lan>
 
On Friday, April 14, 2023 at 10:08:54 AM UTC-4, danny burstein wrote:
In <op.13d81...@ryzen.home> \"Commander Kinsey\" <C...@nospam.com> writes:

In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2.3kW.\"

Why? A UK socket is 13A, or 3.12kW.
I\'ll play the stright cow here. In the USofA, a \"continous load\"
on a circuit is generall maxed at at _80 percent_ of the rated
wire/circuit carrying capcity.

Reason: heat buildup.

I suspect, with no foundationwhatsever, the UK uses
the same concepts.

I\'m no expert in UK electrical regulations, but in other conversations, I\'m pretty sure I\'ve been told this is not the case. The reason is, in the UK, most homes are wired with a \"ring\" that can carry much more than 13 amps. So the wires and breaker are rated at higher currents. So each 13 amp load can actually draw 13 amps.

Also, in the UK, the protection device for everything plugged into an outlet, is in the device. They put a \"fuse\" in the connector itself.

Sounds pretty good to me. In conversations with brits who know about this stuff, they claim their electrical safety is much better than in the US. They don\'t seem to have a problem with tossing out the old every few decades, when they come up with something that is significantly better.

--

Rick C.

- Get 1,000 miles of free Supercharging
- Tesla referral code - https://ts.la/richard11209
 
On Fri, 14 Apr 2023 15:08:47 +0100, danny burstein <dannyb@panix.com> wrote:

In <op.13d81pc2mvhs6z@ryzen.home> \"Commander Kinsey\" <CK1@nospam.com> writes:

In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2.3kW.\"

Why? A UK socket is 13A, or 3.12kW.

I\'ll play the stright cow here.

No idea what that\'s supposed to mean.

In the USofA, a \"continous load\"
on a circuit is generall maxed at at _80 percent_ of the rated
wire/circuit carrying capcity.

Reason: heat buildup.

I suspect, with no foundationwhatsever, the UK uses
the same concepts.

It does not, we wire things properly as we\'re a 1st world country. You can buy 3kW fanheaters for example. I\'ve run one for several hours without anything bursting into flames.

We also have switches on our sockets, and sleeved pins. I guess that\'s why you still have the wimpy 120V in most circuits.
 
On Friday, April 14, 2023 at 3:58:33 PM UTC-4, Commander Kinsey wrote:
On Fri, 14 Apr 2023 15:08:47 +0100, danny burstein <dan...@panix.com> wrote:

In <op.13d81...@ryzen.home> \"Commander Kinsey\" <C...@nospam.com> writes:

In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2.3kW.\"

Why? A UK socket is 13A, or 3.12kW.

I\'ll play the stright cow here.
No idea what that\'s supposed to mean.
In the USofA, a \"continous load\"
on a circuit is generall maxed at at _80 percent_ of the rated
wire/circuit carrying capcity.

Reason: heat buildup.

I suspect, with no foundationwhatsever, the UK uses
the same concepts.
It does not, we wire things properly as we\'re a 1st world country. You can buy 3kW fanheaters for example. I\'ve run one for several hours without anything bursting into flames.

We also have switches on our sockets, and sleeved pins. I guess that\'s why you still have the wimpy 120V in most circuits.

Danny, aren\'t you glad you offered some help?

--

Rick C.

+ Get 1,000 miles of free Supercharging
+ Tesla referral code - https://ts.la/richard11209
 
On 2023-04-14 17:35, Ricky wrote:
On Friday, April 14, 2023 at 10:08:54 AM UTC-4, danny burstein wrote:
In <op.13d81...@ryzen.home> \"Commander Kinsey\" <C...@nospam.com> writes:

In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2.3kW.\"

Why? A UK socket is 13A, or 3.12kW.
I\'ll play the stright cow here. In the USofA, a \"continous load\"
on a circuit is generall maxed at at _80 percent_ of the rated
wire/circuit carrying capcity.

Reason: heat buildup.

I suspect, with no foundationwhatsever, the UK uses
the same concepts.

I\'m no expert in UK electrical regulations, but in other conversations, I\'m pretty sure I\'ve been told this is not the case. The reason is, in the UK, most homes are wired with a \"ring\" that can carry much more than 13 amps. So the wires and breaker are rated at higher currents. So each 13 amp load can actually draw 13 amps.

Also, in the UK, the protection device for everything plugged into an outlet, is in the device. They put a \"fuse\" in the connector itself.

Sounds pretty good to me. In conversations with brits who know about this stuff, they claim their electrical safety is much better than in the US. They don\'t seem to have a problem with tossing out the old every few decades, when they come up with something that is significantly better.

I have an old British plug here, fused. I just opened it for a check,
and the fuse is rated 13A.

With a continuous load of 13A, that fuse will blow. I don\'t know if in
hours, or days, or minutes, but it will blow.

--
Cheers, Carlos.
 
On 14/04/2023 22:34, Carlos E.R. wrote:

I have an old British plug here, fused. I just opened it for a check,
and the fuse is rated 13A.

With a continuous load of 13A, that fuse will blow. I don\'t know if in
hours, or days, or minutes, but it will blow.

I don\'t think that\'s right. A 13A fuse should not blow at 13A, but may
blow above 13A. It may take some time.

--
Cheers
Clive
 
On Friday, April 14, 2023 at 5:50:45 PM UTC-4, Clive Arthur wrote:
On 14/04/2023 22:34, Carlos E.R. wrote:

I have an old British plug here, fused. I just opened it for a check,
and the fuse is rated 13A.

With a continuous load of 13A, that fuse will blow. I don\'t know if in
hours, or days, or minutes, but it will blow.
I don\'t think that\'s right. A 13A fuse should not blow at 13A, but may
blow above 13A. It may take some time.

Why above, but not at 13A? These things are not hugely precise. I know you can\'t count on a 13A fuse to blow at 14A. I would not expect to draw 13A from a 13A circuit and never have problems. I guess if you go through a few 13A fuses, you will eventually find a 13.5A fuse and life will be good.

--

Rick C.

-- Get 1,000 miles of free Supercharging
-- Tesla referral code - https://ts.la/richard11209
 
On Friday, 14 April 2023 at 17:06:12 UTC-7, Ricky wrote:
On Friday, April 14, 2023 at 5:50:45 PM UTC-4, Clive Arthur wrote:
On 14/04/2023 22:34, Carlos E.R. wrote:

I have an old British plug here, fused. I just opened it for a check,
and the fuse is rated 13A.

With a continuous load of 13A, that fuse will blow. I don\'t know if in
hours, or days, or minutes, but it will blow.
I don\'t think that\'s right. A 13A fuse should not blow at 13A, but may
blow above 13A. It may take some time.
Why above, but not at 13A? These things are not hugely precise. I know you can\'t count on a 13A fuse to blow at 14A. I would not expect to draw 13A from a 13A circuit and never have problems. I guess if you go through a few 13A fuses, you will eventually find a 13.5A fuse and life will be good.
....

A UK 13A fuse will actually pass about 20A indefinitely.

https://www.pat-testing-training.net/articles/fuse-operation-characteristics.php

kw
 
On 2023-04-14 23:50, Clive Arthur wrote:
On 14/04/2023 22:34, Carlos E.R. wrote:

I have an old British plug here, fused. I just opened it for a check,
and the fuse is rated 13A.

With a continuous load of 13A, that fuse will blow. I don\'t know if in
hours, or days, or minutes, but it will blow.

I don\'t think that\'s right.  A 13A fuse should not blow at 13A, but may
blow above 13A.  It may take some time.

Fuses are not precision things. For that you need an electromagnetic
current limiter switch. They simply blow faster the higher the current
is. Given time, they will eventually blow even at half the rated current.

--
Cheers, Carlos.
 
On 14-Apr-23 11:57 pm, Commander Kinsey wrote:
In the UK, \"most vehicle manufacturers limit the current drawn from a
standard domestic 3 pin socket to 10A or less, which equates to a
maximum of 2.3kW.\"

Why?  A UK socket is 13A, or 3.12kW.

Commonality with other 230/240V markets? The UK is unusual in having
standard sockets rated at more than 10A.

Sylvia.
 
On Friday, April 14, 2023 at 8:47:02 PM UTC-4, ke...@kjwdesigns.com wrote:
On Friday, 14 April 2023 at 17:06:12 UTC-7, Ricky wrote:
On Friday, April 14, 2023 at 5:50:45 PM UTC-4, Clive Arthur wrote:
On 14/04/2023 22:34, Carlos E.R. wrote:

I have an old British plug here, fused. I just opened it for a check,
and the fuse is rated 13A.

With a continuous load of 13A, that fuse will blow. I don\'t know if in
hours, or days, or minutes, but it will blow.
I don\'t think that\'s right. A 13A fuse should not blow at 13A, but may
blow above 13A. It may take some time.
Why above, but not at 13A? These things are not hugely precise. I know you can\'t count on a 13A fuse to blow at 14A. I would not expect to draw 13A from a 13A circuit and never have problems. I guess if you go through a few 13A fuses, you will eventually find a 13.5A fuse and life will be good.
...

A UK 13A fuse will actually pass about 20A indefinitely.

https://www.pat-testing-training.net/articles/fuse-operation-characteristics.php

kw

I stand corrected.

--

Rick C.

-+ Get 1,000 miles of free Supercharging
-+ Tesla referral code - https://ts.la/richard11209
 
On Sat, 15 Apr 2023 11:03:26 +1000, Sylvia Else, another brain dead,
troll-feeding, senile ASSHOLE, blathered again:


> Commonality with other 230/240V markets?

More like him trolling the shit out of these ngs again, you brain dead,
troll-feeding senile ASSHOLE!
 
On 15/04/2023 02:03, Sylvia Else wrote:
On 14-Apr-23 11:57 pm, Commander Kinsey wrote:
In the UK, \"most vehicle manufacturers limit the current drawn from a
standard domestic 3 pin socket to 10A or less, which equates to a
maximum of 2.3kW.\"

Why?  A UK socket is 13A, or 3.12kW.

Commonality with other 230/240V markets? The UK is unusual in having
standard sockets rated at more than 10A.

Although they are nominally rated at 13A modern sockets are seldom happy
with anything much beyond 10A as a continuous load. I have seen plenty
of extension sockets destroyed by having a fan heater plugged in.

In a cold room a 3kW fan heater doesn\'t switch it off until the
thermostat is satisfied which can be a few hours by which time the
plastic around the socket has melted.

At full 13A load current for an extended period plugs can also get
uncomfortably hot due to the UK having a mains fuse in them.

Short term 3kW loads are OK like kettles for a few minutes (but even
that is now deprecated all modern kettles are 2.4kW aka 10A).

I suspect that they use less beryllium in the spring contacts than they
did in the old days when nominally 13A sockets were real 13A sockets.

--
Martin Brown
 
On Friday, April 14, 2023 at 3:58:33 PM UTC-4, Commander Kinsey wrote:
On Fri, 14 Apr 2023 15:08:47 +0100, danny burstein <dan...@panix.com> wrote:

In <op.13d81...@ryzen.home> \"Commander Kinsey\" <C...@nospam.com> writes:

In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2.3kW.\"

Why? A UK socket is 13A, or 3.12kW.

I\'ll play the stright cow here.
No idea what that\'s supposed to mean.
In the USofA, a \"continous load\"
on a circuit is generall maxed at at _80 percent_ of the rated
wire/circuit carrying capcity.

Reason: heat buildup.

I suspect, with no foundationwhatsever, the UK uses
the same concepts.
It does not, we wire things properly as we\'re a 1st world country. You can buy 3kW fanheaters for example. I\'ve run one for several hours without anything bursting into flames.

UK adopted the ring circuit for residential wiring as a measure to conserve copper which was expensive and in short supply in the 1940s. It is not better.

We also have switches on our sockets, and sleeved pins. I guess that\'s why you still have the wimpy 120V in most circuits.

Much of UK wiring would not be allowed under the national electric code in the U.S. For one would be this crummy ring circuit idea. U.S requires at least two independently fused/ protected circuits per room, UK puts an entire floor on the ring circuit. U.S. not only allows for, but requires, many more electrical outlets than UK. If they try doing the equivalent number on a ring circuit, they would be begging for nuisance trips. Sounds like the ring circuit method has been abandoned for new construction in UK for quite some time.

UK is not exactly famous for high quality housing of any kind, actually the place is a disaster area.
 
On Friday, April 14, 2023 at 11:35:25 AM UTC-4, Ricky wrote:
On Friday, April 14, 2023 at 10:08:54 AM UTC-4, danny burstein wrote:
In <op.13d81...@ryzen.home> \"Commander Kinsey\" <C...@nospam.com> writes:

In the UK, \"most vehicle manufacturers limit the current drawn from a standard domestic 3 pin socket to 10A or less, which equates to a maximum of 2.3kW.\"

Why? A UK socket is 13A, or 3.12kW.
I\'ll play the stright cow here. In the USofA, a \"continous load\"
on a circuit is generall maxed at at _80 percent_ of the rated
wire/circuit carrying capcity.

Reason: heat buildup.

I suspect, with no foundationwhatsever, the UK uses
the same concepts.
I\'m no expert in UK electrical regulations, but in other conversations, I\'m pretty sure I\'ve been told this is not the case. The reason is, in the UK, most homes are wired with a \"ring\" that can carry much more than 13 amps.. So the wires and breaker are rated at higher currents. So each 13 amp load can actually draw 13 amps.

Also, in the UK, the protection device for everything plugged into an outlet, is in the device. They put a \"fuse\" in the connector itself.

Sounds pretty good to me. In conversations with brits who know about this stuff, they claim their electrical safety is much better than in the US. They don\'t seem to have a problem with tossing out the old every few decades, when they come up with something that is significantly better.

As usual for you, you don\'t have a hint in hell what you\'re talking about, and you\'re completely wrong.

Of course the ring circuit has more capacity, it\'s nearly powering the whole damned house. So, unless they want to up the fault current tolerance of every single thing they plug into it, and thus increase the cost significantly, they have to be fused at lower current.

--

Rick C.