There are 2 major differences between the European and US electric systems:
(I use here layman language for comprehensibility)
1. The 240V US voltage is obtained by using two 120V voltages, 180 degree
out of phase from each other and connecting the load between them, thus
summing the voltages. In Europe the residential 220V is a single phase; one
terminal is equivalent to the US white wire, the other to the black wire,
only that the voltage is 83% higher.
2. The frequency in US is 60Hz and in Europe is 50Hz. When the same voltage
is applied, this causes AC-motors to overheat, because the an iron core is
designed for 60Hz and will saturate at 50Hz . To avoid the iron core
saturation at 50Hz one has to decrease the voltage to 50/60 x 240= 200V .
Now to your problem. This solution is only HYPOTHETICAL! One could connect
the European 220V to the BLACK and RED and create an "artificial" WHITE
using an insulation-transformer, with the primary connected to the 220V
(BLACK and RED) and the secondary, at 120V, connected one side to BLACK and
the other to WHITE (it must be an insulation transformer, not an
autotransformer for safety reasons). Because I do not know if the
electronics (supplied by the 120V) in the dryer is sensitive to phase
differences between BLACK and RED, I cannot tell you if it will work. What
is left is now the issue with the motor overheating, which perhaps will not
be excessive with just 10% voltage (200V to 220V). If you are willing to
experiment assisted by an electrician that knows the local code...that is
OK, but of course all the cautions and warnings do apply.
Gene
P.S. I appreciate comments from fellow EE's particularly regarding the
safety and the overheating issues.
(I use here layman language for comprehensibility)
1. The 240V US voltage is obtained by using two 120V voltages, 180 degree
out of phase from each other and connecting the load between them, thus
summing the voltages. In Europe the residential 220V is a single phase; one
terminal is equivalent to the US white wire, the other to the black wire,
only that the voltage is 83% higher.
2. The frequency in US is 60Hz and in Europe is 50Hz. When the same voltage
is applied, this causes AC-motors to overheat, because the an iron core is
designed for 60Hz and will saturate at 50Hz . To avoid the iron core
saturation at 50Hz one has to decrease the voltage to 50/60 x 240= 200V .
Now to your problem. This solution is only HYPOTHETICAL! One could connect
the European 220V to the BLACK and RED and create an "artificial" WHITE
using an insulation-transformer, with the primary connected to the 220V
(BLACK and RED) and the secondary, at 120V, connected one side to BLACK and
the other to WHITE (it must be an insulation transformer, not an
autotransformer for safety reasons). Because I do not know if the
electronics (supplied by the 120V) in the dryer is sensitive to phase
differences between BLACK and RED, I cannot tell you if it will work. What
is left is now the issue with the motor overheating, which perhaps will not
be excessive with just 10% voltage (200V to 220V). If you are willing to
experiment assisted by an electrician that knows the local code...that is
OK, but of course all the cautions and warnings do apply.
Gene
P.S. I appreciate comments from fellow EE's particularly regarding the
safety and the overheating issues.