<phil-news-nospam@ipal.net> wrote in message
news:bu2quj12cse@enews4.newsguy.com...
mixed residential and
commercial areas where the primary need was for 120/240 single phase and
perhaps a single 3 phase user
such as a deli or gas station that used 3 phase motors for refrigeration or
air compressor. In these cases, the
configuration was typically open delta with a smaller transformer for the
additional 3 phase requirement
news:bu2quj12cse@enews4.newsguy.com...
Interestingly enough, though, is that where I have commonly seen this isIn sci.electronics.basics Louis Bybee <louistroutbybee@comcasttrout.net
wrote:
| Something close to what you describe is commonly available in many areas
of
| the US. 240 volt 3 phase in a delta configuration with one transformer
| center tapped for a grounded neutral to provide 120 volts for lighting,
and
| receptacle load, and three phase 240 volts for motor load or high
capacity
| heating loads. The transformers can consist of three individual units
with
| the center tapped one providing 120 volts being much larger than the
other
| two, or an "Open Delta" three phase configuration utilizing two
| transformers. It is very common in residential, office, and light
industrial
| areas. It can be superior where there is motor load, and 480 Y 277 isn't
| available. Unless motors are specifically rated for 208 volts there can
be
| significant power loss, and heating from the reduced operating voltage.
The problem with this configuration is that the 1 phase loads are limited
to about 5% of the total KVA capacity of the transformer. It's fine for
industrial users that have huge amounts of 3 phase need compared to the
lighting/office needs.
mixed residential and
commercial areas where the primary need was for 120/240 single phase and
perhaps a single 3 phase user
such as a deli or gas station that used 3 phase motors for refrigeration or
air compressor. In these cases, the
configuration was typically open delta with a smaller transformer for the
additional 3 phase requirement
There are 277 volt lighting systems available, too, for those with
480Y/277.
But if your 1 phase load is a big part of your total, yet you still need 3
phase power for some big motors, my idea can achieve that and let you go
beyond the 5% limit on the 1 phase loads.
I am all too aware of the issue where equipment designed for 240 volts
just
can't do the job on 208 volts. In many cases things have to be derated,
such
as less HP in motors, and longer warm up times for ovens. In worse cases,
there can be failure (motor burnout due to overheating due to either
stalls
or excessive start current times). Getting 240 for what needs 240, under
the need also for 3 phase for other equipment, or because that's just how
the power is provided (utilities often don't provide 1 phase if your load
is more than 400 to 600 amps).
--
--------------------------------------------------------------------------
---