On Thu, 11 Oct 2012 21:40:22 -0700, Jeff Liebermann <jeffl@cruzio.com>
wrote:
commercial Li-Ion charger design. As part of the process I did a fair
number of charge/discharge tests of packs on an automated HP rig, and
obtained some interesting insight. Typically laptops (then) used 4v20
as their CLCV regime voltage limit. Reducing this to say 4v10 would
lose them roughly 20% of runtime (your link suggests a smaller
difference than we saw) but increase the cell lifetime by a very
worthwhile amount. If customers had this option I'm sure all the
thinking ones whose personal $$$ were involved would opt for the lower
voltage.
outage patters are in their area.
need for the UPS manufacturers to actually do contemporary designs
instead of churning out 80's technology, and I'm being kind there.
Note though that with Li-xx the "coulomb efficiency" on charge is
around 98% on our testing (admittedly with new cells with less than 20
cycles) compared to the <80% for say NiXX and probably <90% for SLA's.
The difference between those numbers and 100% obviously appears as
heat I could well be wrong, but it seemed during our Li-Ion cycle
testing that the heat dissipated during charge from that ~2% loss
wasn't reflected in a rise in cell casing temp. Maybe the chemical
change during charge is a tad exothermic? Either way, there isn't the
temperature issue with Li-Ion in their *electrical* role that one
experiences with other chemistries - laptops being a perfect example
of how heat from OTHER parts/devices causes the high temp battery
environment. Equally noteworthy is the absence of a float charge
current in Li-xx charge regimes.
If Li-Ion packs were:
(a) oversized - to keep DOD to less than 50% (and enforced by a higher
than 3v0/cell shutoff point);
(b) kept external to the UPS and its heat generation; and
(c) maintained by a sensible charge circuit
then they would be reasonably suitable for UPS duty. I doubt the
average SLA would match them for cycle life in that scenario.
wrote:
A prime spec for laptops is runtime on battery. Years ago I did aOn Fri, 12 Oct 2012 10:14:58 +0800, who where <noone@home.net> wrote:
Just as laptops do ...
The joy of specmanship. If I'm lucky, and can find a way to reduce
charge current or float voltage limit in software, I can usually
extend the battery life. However, that's often impossible without
inside information or reverse engineering. I see far too many laptops
eat batteries due to overheating and overcharging in laptops that have
never been run on battery power.
commercial Li-Ion charger design. As part of the process I did a fair
number of charge/discharge tests of packs on an automated HP rig, and
obtained some interesting insight. Typically laptops (then) used 4v20
as their CLCV regime voltage limit. Reducing this to say 4v10 would
lose them roughly 20% of runtime (your link suggests a smaller
difference than we saw) but increase the cell lifetime by a very
worthwhile amount. If customers had this option I'm sure all the
thinking ones whose personal $$$ were involved would opt for the lower
voltage.
Exactly. Most customers have a better than generic idea of what powerThey also tend to recharge rather quickly, in order to deal with
repetitive power failures.
Yes, almost universally.
I've often wondered if there's a recharge time spec for UPS's. A few
quick Google searches didn't find anything. I can see why the UPS
manufacturers would want to recharge quickly, but they should at least
give the customer the choice between fast recharge and long battery
life.
outage patters are in their area.
The first answer to your rhetorical question would be price and theI have been called on to "service" quite a number of failed soho UPS'
of varying sizes from 150W to 4kW, mostly APC. The electronics are
almost universally fine - except for one with dead FETs in the
inverter, the failure mode in every single one was batteries. When I
bothered to check the charge regime, it was found to implement the
above rules 1 and 3 on how to kill UPS batteries.
Yep. I've had similar experiences. I don't see many big UPS's but
overcharging is epidemic on small UPS's.
Rhetorical question:
Why are there no UPS's that use Li-Ion batteries?
Spoiler:
http://batteryuniversity.com/learn/article/how_to_prolong_lithium_based_batteries
need for the UPS manufacturers to actually do contemporary designs
instead of churning out 80's technology, and I'm being kind there.
Note though that with Li-xx the "coulomb efficiency" on charge is
around 98% on our testing (admittedly with new cells with less than 20
cycles) compared to the <80% for say NiXX and probably <90% for SLA's.
The difference between those numbers and 100% obviously appears as
heat I could well be wrong, but it seemed during our Li-Ion cycle
testing that the heat dissipated during charge from that ~2% loss
wasn't reflected in a rise in cell casing temp. Maybe the chemical
change during charge is a tad exothermic? Either way, there isn't the
temperature issue with Li-Ion in their *electrical* role that one
experiences with other chemistries - laptops being a perfect example
of how heat from OTHER parts/devices causes the high temp battery
environment. Equally noteworthy is the absence of a float charge
current in Li-xx charge regimes.
If Li-Ion packs were:
(a) oversized - to keep DOD to less than 50% (and enforced by a higher
than 3v0/cell shutoff point);
(b) kept external to the UPS and its heat generation; and
(c) maintained by a sensible charge circuit
then they would be reasonably suitable for UPS duty. I doubt the
average SLA would match them for cycle life in that scenario.