William Sommerwerck wrote:
Uh... In the MOV?

I thought the MOV conducted above its breakdown voltage (generally around
300V), and the energy in the section of the AC waveform above that voltage
heated up the MOV.

Am I missing something?
In your typical plug in suppressor mounted next to the computer
for example. The job of the MOV is to clamp the maximum voltage
across the "protected" outlets. That it does this fairly quickly
is what hopefully protect the equipment, while at the same time
drawing enough current through the house wiring to either pop
the fuse or circuit breaker at the suppressor or back at the
service panel.

What the plug-in suppressors rely on is the impedance (generally
inductive) in the house wiring to limit the rise time of the
surge until the circuit breaker (or fusable parts) have time to
react by opening up.

The term joules can be described as Watt Seconds. And the ability
to deal with it is based on the fault (or surge) being over, or
the circuit breakers upstream open before the device self
destructs.

Whole house protectors work the same way in that they shunt the
current to ground safely before it has a chance to cause a
destructive rise to the rest of the house wiring.

Jeff



--
“Egotism is the anesthetic that dulls the pain of stupidity.”
Frank Leahy, Head coach, Notre Dame 1941-1954

http://www.stay-connect.com
 
I thought the MOV conducted above its breakdown voltage (generally
around 300V), and the energy in the section of the AC waveform above
that voltage heated up the MOV.

Am I missing something?

Ohm's Law:
If the MOV conducts at a low resistance, the power it dissipates will be
minimal. Thus, the surge energy gets dissipated in whatever ground it's
shunted to.
How low is low?

I suspect that's not a complete explanation, but I won't argue at this time.
 
Jim Yanik wrote:
"William Sommerwerck" <grizzledgeezer@comcast.net> wrote in
news:hvigjf$hg7$1@news.eternal-september.org:

It is bud's job to constantly promote lies and myths. He is paid
to promote plug-in protectors. Lying is what promoters may do.
Where are those numeric specs? bud will never provide any.
He cannot claim protection that does not exist.
Where does that energy dissipate? bud cannot say. Otherwise
he must admit that plug-in protectors are profit centers – not
protection.
Uh... In the MOV?

I thought the MOV conducted above its breakdown voltage (generally
around 300V), and the energy in the section of the AC waveform above
that voltage heated up the MOV.

Am I missing something?

Ohm's Law.
If the MOV conducts at a low resistance,the power it dissipates will be
minimal.
Thus,the surge energy gets dissipated in whatever ground it's shunted to.


Bullshit. The Mov dissipates (Umov)*I*T, or
Total Energy=MOVvolts * Current * Seconds.
Or integrate over those values, if they vary in time.
The Mov voltage does NOT drop to zero, when conducting.
Where did you learn about electricity??????
Of course some currents might be enough to blow the MOV,
and that is specified in the documentation, as in how
many WATTseconds blows it to pieces.
Even then it still might provide protection, although
only once, and then blow the mains fuse.
 
Many years ago, PC and/or Byte (I forget which) used to test suppressors.
If
they failed to provide suppression, I assume the mag would have said so.

hillarious, PC magazine is your source for the lowdown on surge supression
devices?
It was, 20 years ago. I don't think you get the point, though.
 
Sjouke Burry <burrynulnulfour@ppllaanneett.nnll> wrote in
news:4c1d48fd$0$14115$703f8584@textnews.kpn.nl:

Jim Yanik wrote:
"William Sommerwerck" <grizzledgeezer@comcast.net> wrote in
news:hvigjf$hg7$1@news.eternal-september.org:

It is bud's job to constantly promote lies and myths. He is paid
to promote plug-in protectors. Lying is what promoters may do.
Where are those numeric specs? bud will never provide any.
He cannot claim protection that does not exist.
Where does that energy dissipate? bud cannot say. Otherwise
he must admit that plug-in protectors are profit centers – not
protection.
Uh... In the MOV?

I thought the MOV conducted above its breakdown voltage (generally
around 300V), and the energy in the section of the AC waveform above
that voltage heated up the MOV.

Am I missing something?

Ohm's Law.
If the MOV conducts at a low resistance,the power it dissipates will
be minimal.
Thus,the surge energy gets dissipated in whatever ground it's shunted
to.


Bullshit. The Mov dissipates (Umov)*I*T, or
Total Energy=MOVvolts * Current * Seconds.
Or integrate over those values, if they vary in time.
The Mov voltage does NOT drop to zero, when conducting.
I never said it did.
the MOV voltage rating is the voltage when it changes state and drops to a
low resistance to shunt the surge to GROUND.
Now,how low a resistance in the conducting state is another matter.
that's dependent on the MOV design/ratings.


Where did you learn about electricity??????
USAF PME School,1971.

Of course some currents might be enough to blow the MOV,
yes,I said the MOV's dissipation would be "minimal",....compared to the
total energy the MOV was passing to ground.
what energy the MOV dissipates can easily be enough to blow it apart.
I've seen it happen many times.
But the MOV is not dissipating the total energy of the surge with it's
suicide.

and that is specified in the documentation, as in how
many WATTseconds blows it to pieces.
Even then it still might provide protection, although
only once, and then blow the mains fuse.
Of course,the fuse itself can arc over in a lightning strike,as it
can exceed the typical 250v voltage rating of the fuse.

--
Jim Yanik
jyanik
at
localnet
dot com
 
Bullshit. The Mov dissipates (Umov)*I*T, or
Total Energy=MOVvolts * Current * Seconds.
Or integrate over those values, if they vary in time.
The Mov voltage does NOT drop to zero, when conducting.

I never said it did.
the MOV voltage rating is the voltage when it changes
state and drops to a
low resistance to shunt the surge to GROUND.
Now,how low a resistance in the conducting state is
another matter.
that's dependent on the MOV design/ratings.


Where did you learn about electricity??????

USAF PME School,1971.

Of course some currents might be enough to blow the MOV,

yes,I said the MOV's dissipation would be
"minimal",....compared to the
total energy the MOV was passing to ground.
what energy the MOV dissipates can easily be enough to
blow it apart.
I've seen it happen many times.
But the MOV is not dissipating the total energy of the
surge with it's
suicide.

Jim Yanik
jyanik
at
localnet
dot com
A MOV is somewhat like two back-to-back Zener diodes. It is
a voltage clamp. You do not pass energy to ground, you pass
current to ground just like you do with any load. The energy
is totally dissipated in the MOV.

David
 
William Sommerwerck <grizzledgeezer@comcast.net> wrote:
It is bud's job to constantly promote lies and myths. He is paid
to promote plug-in protectors. Lying is what promoters may do.
Where are those numeric specs? bud will never provide any.
He cannot claim protection that does not exist.

Where does that energy dissipate? bud cannot say. Otherwise
he must admit that plug-in protectors are profit centers ? not
protection.

Uh... In the MOV?

I thought the MOV conducted above its breakdown voltage (generally around
300V), and the energy in the section of the AC waveform above that voltage
heated up the MOV.

Am I missing something?

Many years ago, PC and/or Byte (I forget which) used to test suppressors. If
they failed to provide suppression, I assume the mag would have said so.
hillarious, PC magazine is your source for the lowdown on surge supression
devices?
 
William Sommerwerck <grizzledgeezer@comcast.net> wrote:
Many years ago, PC and/or Byte (I forget which) used to test suppressors.
If
they failed to provide suppression, I assume the mag would have said so.

hillarious, PC magazine is your source for the lowdown on surge supression
devices?

It was, 20 years ago. I don't think you get the point, though.
So what is the point? John Dvorak wrote a story about surge supressors and
how they worked with his Cumulus 386 laptop and his CompuAdd 486sx tower?
 
"Cydrome Leader" <presence@MUNGEpanix.com> wrote in message
news:hvk9c7$hrm$2@reader1.panix.com...
William Sommerwerck <grizzledgeezer@comcast.net> wrote:

Many years ago, PC and/or Byte (I forget which) used to test
suppressors.
If they failed to provide suppression, I assume the mag would have said
so.

Hilarious, PC magazine is your source for the lowdown on surge
supression
devices?

It was, 20 years ago. I don't think you get the point, though.

So what is the point? John Dvorak wrote a story about surge supressors and
how they worked with his Cumulus 386 laptop and his CompuAdd 486sx tower?
The point is that they were performing lab tests on the suppressors. These
tests included determining the clamping voltage. (I don't remember if they
were tested to destruction.) The tests were presumably performed in
accordance with industry-accepted standards.
 
westom wrote:
On Jun 18, 3:55 pm, bud-- <remove.budn...@isp.com> wrote:
Still missing - your source that says plug-in suppressors are NOT
effective - just like westom.
And westom has been looking for years.

Your job is to promote plug-in protectors.
Poor westom just keeps repeating the same lies, just like Josef Goebbels.

If he had valid technical arguments he would not have to try to
discredit those that expose his drivel.

My only association with surge suppressors is that I have 2 of them.

You
cannot even post any spec numbers that define protection from each
type of surge.
"Each type of surge" is more nonsense. SquareD, amongst others, does not
have specs for "each type of surge".

I provided a link to the specs I have provided in many threads -always
ignored by westom, just like he ignores anything that conflicts with his
religious belief in earthing.

Apparently poor westom believes plug-in suppressors do not work, so he
believes specs cannot possibly exist.

Destructive surges are hundreds of thousands of joules. Where does
that energy dissipate? Bud says that energy just magically
disappears.
Poor westom's religious blinders prevent him from seeing what has been
said in this thread, and numerous other threads.

For incoming power wires, at about 6kV there is arc over from service
busbars to the enclosure. After the arc stabilized the arc is hundreds
of volts. The enclosure is connected to the earthing electrodes, so this
dumps the vast majority of the incoming surge energy to earth. The
neutral (in the US) is also always tied to the system ground at the
service, so energy coming in on the neutral is directly earthed.
Apparently that is all magic for westom.

For a plug-in suppressor, the impedance of the branch circuit wiring
greatly limits the current that can reach the suppressor. That greatly
limits the energy that can reach the suppressor. NIST surge guru
Martzloff looked at the energy that could reach the suppressor and was
surprised that it was 35 joules or less. In most of his tests it was
under 1 joule. That is with service surges up to the maximum that there
is any reasonable probability of occurring.

As Sjouke wrote, the MOV dissipates an energy equal to the clamp voltage
times the current times the time. For a plug-in suppressor the current
is very limited by the branch circuit impedance. And the time is very
short - well under 100 microseconds. Fuses or circuit breakers do not
provide protection because they are nowhere near fast enough - they
won't open during a surge.

Plug-in suppressors do not work primarily by earthing a surge - that
reason poor westom believes they do not work. The IEEE surge guide
explains how they work (starting pdf page40). They clamp the voltage on
all wires to the ground at the suppressor. The voltage between all wires
going to the protected equipment is safe for the protected equipment.

Service panel suppressors also work by clamping the voltage - from hot
wires to ground/earthing electrode (and hot-to-hot). Because the current
can be up to 10,000A per hot (essentially zero probability of higher
current, at least for houses) they can dissipate significant energy. But
the vast majority of the energy is dissipated in the earth by the
service earth electrode connection. The largest surges (lightning) are
under 100 microseconds. Suppressors are readily available that will
provide protection. With thousands of amps to the earthing electrode,
the potential of the building "ground" can rise far above "absolute"
earth potential.

Neither service panel suppressors or plug-in suppressors protect by
absorbing the surge energy. But in the process of protecting, some of
the energy is absorbed.

MOVs are fast enough to protect from the fastest surge. And if there was
an extremely fast rise time it would be lowered by the impedance of the
source wiring.

All of the above is from NIST expert Martzloff, or other experts in the
field.

westom ignores it all.

Bud's citation Page 42 Figure 8 shows a surge earthed 8000 volts
destructively through a nearby TV.
The lie repeated. Poor westom tries to make an example that explains
protection say the opposite.

The plug-in suppressor in this IEEE surge guide example protects the TV
connected to it. It lowers the surge voltage at a second TV, although
its job is to protect the equipment connected to it. It is a lie that
the suppressor at TV1 damages TV2.

The point of the illustration for the IEEE, and anyone who can think, is
"to protect TV2, a second multiport protector located at TV2 is required."

Why?
The house did not earth via a 'whole
house' protector.
In the IEEE example the surge comes in on the cable service, and high
voltage results from a ground wire that is too long. westomn's favored
service panel suppressor would provide absolutely *NO* protection. The
IEEE says, for distant entrance points, that "the only effective way of
protecting the equipment is to use a multiport [plug-in] protector."

A protector is
only as effective as its earth ground.
westom's religious mantra protects him from conflicting thoughts (aka
reality).
westom is the poster child for cognitive dissonance.

Still never explained - why aren't flying airplanes crashing every day
when they are hit by lightning?

He is paid to
promote plug-in protectors.
The lie repeated.

But still never seen - any reliable source that agrees with westom that
plug-in suppressors are NOT effective.

Still never seen - answers to simple questions:
- Why do the only 2 examples of protection in the IEEE guide use plug-in
suppressors?
- Why does the NIST guide says plug-in suppressors are "the easiest
solution"?
- Why does the NIST guide say "One effective solution is to have the
consumer install" a multiport plug-in suppressor?
- How would a service panel suppressor provide any protection in the
IEEE example, page 42?
- Why does the IEEE guide say for distant service points "the only
effective way of protecting the equipment is to use a multiport
[plug-in] protector"?
- Why did Martzloff say in his paper "One solution. illustrated in this
paper, is the insertion of a properly designed [multiport plug-in surge
suppressor]"?
- Why does Dr. Mansoor support multiport plug-in suppressors?
- Why does "responsible" manufacturer SquareD says "electronic
equipment may need additional protection by installing plug-in
[suppressors] at the point of use"?
- Why don’t favored SquareD service panel suppressors list "each type of
surge"?

For real science read the IEEE and NIST surge guides. Both say plug-in
suppressors are effective.

The IEEE guide, in particular, is really an excellent source of
information from a reliable source. I really recommend anyone who is
interested in surge protection read it.

--
bud--
 
On Jun 19, 8:20 pm, "David" <some...@somewhere.com> wrote:
A MOV is somewhat like two back-to-back Zener diodes. It is
a voltage clamp. You do not pass energy to ground, you pass
current to ground just like you do with any load. The energy
is totally dissipated in the MOV.
Now do the numbers. How does that hundred joule MOV absorb energy
that is hundreds of thousands of joules? You are reciting the myths
promoted by plug-in protectors.

For example, how to get the protector to last longer? Increase its
joules rating. Then the entire protector absorbs "LESS" energy.
Protector that absorbs a surge is the urban myth promoted by those who
never learned this stuff. This 100 years old technology.

So that energy dissipates harmlessly in earth - not inside the
building - the protector must make a short ('less than 10 foot')
connection to single point earth ground. No protector is protection.
None. A protector is only a connecting device. Either it connects a
20,000 amp surge harmlessly to earth. Or it does nothing. A
protector is only as effective as its earth ground - which those
educated by advertising never learn.
 
On Jun 19, 12:25 pm, Jeffrey D Angus <jan...@suddenlink.net> wrote:
What the plug-in suppressors rely on is the impedance (generally
inductive) in the house wiring to limit the rise time of thesurgeuntil the circuit breaker (or fusable parts) have time to
react by opening up.
No surge protector is too slow. That wiring is why plug-in
protectors are not earthed. And why Bud will not discuss wire
impedance and earth ground.

bud's citation Page 42 Figure 8 shows a plug-in protecting earthing
a surge 8000 volts destructively through a nearby TV. He hopes you do
not grasp the point in his IEEE citation.

So let's put numbers to it. Let's say the plug-in protector and TV
are 50 feet of wire from the breaker box. That means it is less than
0.2 ohms resistance. And maybe 120 ohms impedance. So that protector
will earth a trivial 100 amp surge? 100 amps times 120 ohms means the
protector and TV are at maybe 12,000 volts. Why did the protector
earth that surge 8000 volts through the TV? AC electric wire
impedance meant the surge had to obtain earth 8000 volts destructively
through the TV.

Why do telcos all over the world not waste money on bud's plug-in
protectors? Because telcos can suffer about 100 surges per
thunderstorm. So telcos put a protector as close to earth ground as
possible. And up to 50 meters separated from electronics. That
separation means increases protection. Why? See numbers in that
above paragraph.

Whereas an average homeowner suffers maybe one surge every seven
years. A telco suffers at least 100 with each storm. So telcos do
not locate protectors adjacent to electronics. Telcos always earth
'whole house' protectors for the same reasons it was done 100 year ago
– a low impedance connection to single point ground. Protector must
be as close to earth as possible (lowest impedance to single point
ground) AND works best when distant from electronics.

Learn that no protector works by absorbing energy. That is why the
protector too close to appliances and too far from earth ground can
even earth that surge 8000 volts destructively through a nearby TV. A
majority only believe the advertising myths - that protectors
magically make hundreds of thousands of joules just magically
disappear. That myth sells plug-in protectors. Any location that
cannot have damage (ie munitions dumps) instead earths a 'whole house'
protector. Then energy never enters a building. Then energy
harmlessly dissipates outside the building in earth ground.

Protection is always about where energy dissipates. IOW a protector
is only as effective as its earth ground. A reality that would harm
bud's profit margins.
 
"David" <someone@somewhere.com> wrote in news:hvjmsg$4v4$1@news.eternal-
september.org:

Bullshit. The Mov dissipates (Umov)*I*T, or
Total Energy=MOVvolts * Current * Seconds.
Or integrate over those values, if they vary in time.
The Mov voltage does NOT drop to zero, when conducting.

I never said it did.
the MOV voltage rating is the voltage when it changes
state and drops to a
low resistance to shunt the surge to GROUND.
Now,how low a resistance in the conducting state is
another matter.
that's dependent on the MOV design/ratings.


Where did you learn about electricity??????

USAF PME School,1971.

Of course some currents might be enough to blow the MOV,

yes,I said the MOV's dissipation would be
"minimal",....compared to the
total energy the MOV was passing to ground.
what energy the MOV dissipates can easily be enough to
blow it apart.
I've seen it happen many times.
But the MOV is not dissipating the total energy of the
surge with it's
suicide.

Jim Yanik
jyanik
at
localnet
dot com

A MOV is somewhat like two back-to-back Zener diodes. It is
a voltage clamp.
no,it's not. it does not "clamp" the voltage.

You do not pass energy to ground, you pass
current to ground just like you do with any load. The energy
is totally dissipated in the MOV.

David
totally wrong.
Wiki has a nice article on metal-oxide varistor,I suggest you read it.

--
Jim Yanik
jyanik
at
localnet
dot com
 
"William Sommerwerck" <grizzledgeezer@comcast.net> wrote in
news:hvl00i$lma$1@news.eternal-september.org:

"Cydrome Leader" <presence@MUNGEpanix.com> wrote in message
news:hvk9c7$hrm$2@reader1.panix.com...
William Sommerwerck <grizzledgeezer@comcast.net> wrote:

Many years ago, PC and/or Byte (I forget which) used to test
suppressors.
If they failed to provide suppression, I assume the mag would have
said
so.

Hilarious, PC magazine is your source for the lowdown on surge
supression
devices?

It was, 20 years ago. I don't think you get the point, though.

So what is the point? John Dvorak wrote a story about surge
supressors and how they worked with his Cumulus 386 laptop and his
CompuAdd 486sx tower?

The point is that they were performing lab tests on the suppressors.
These tests included determining the clamping voltage. (I don't
remember if they were tested to destruction.) The tests were
presumably performed in accordance with industry-accepted standards.
"clamping" is a misuse of the word WRT surge protectors.
It misleads people,as in "david" s post.

"trigger voltage" might more accurate.

--
Jim Yanik
jyanik
at
localnet
dot com
 
A MOV is somewhat like two back-to-back Zener diodes. It
is
a voltage clamp.

no,it's not. it does not "clamp" the voltage.

You do not pass energy to ground, you pass
current to ground just like you do with any load. The
energy
is totally dissipated in the MOV.

David




totally wrong.
Wiki has a nice article on metal-oxide varistor,I suggest
you read it.

--
Jim Yanik
jyanik
at
localnet
dot com
Jim, I am not going to get into a flame war over this topic.
Maybe you should check this out:

<http://www.cliftonlaboratories.com/metal_oxide_varistor_(mov).htm>

David
 
David wrote:
http://www.cliftonlaboratories.com/metal_oxide_varistor_(mov).htm
Amazing coincidence that they act much like the old NE-2 neon
bulb across the antenna leads of old receivers for protection.

They would conduct around 65 volts and suddenly go to near
zero impedance, safely shunting what ever energy on the antenna
line to ground.

And although most receiver inputs couldn't handle a steady state
of 65 volts (or 130 vpp), they could handle them long enough for
the neon bulb to conduct and then shunt them to ground.


Jeff


--
“Egotism is the anesthetic that dulls the pain of stupidity.”
Frank Leahy, Head coach, Notre Dame 1941-1954

http://www.stay-connect.com
 
http://www.cliftonlaboratories.com/metal_oxide_varistor_(mov).htm

David
Hi,

I've been following this thread, and I got to wondering are there any
accepted methods to tell if a surge arrestor setup is still usable as
such? I've got a couple industrial 3-phase units that I'd like to
hook up to protect my incoming power, and though they pass the sniff
test I haven't quite convinced myself to add them to the electrical
panel yet. I only have single phase (in the US), but figure that gives
me a spare module that would just be left disconnected.

Anyone have any recommendations or guidance to lend?

Thanks,
Mike
 
"David" <someone@somewhere.com> wrote in news:hvlq34$3ic$1@news.eternal-
september.org:

A MOV is somewhat like two back-to-back Zener diodes. It
is
a voltage clamp.

no,it's not. it does not "clamp" the voltage.

You do not pass energy to ground, you pass
current to ground just like you do with any load. The
energy
is totally dissipated in the MOV.

David




totally wrong.
Wiki has a nice article on metal-oxide varistor,I suggest
you read it.

--
Jim Yanik
jyanik
at
localnet
dot com

Jim, I am not going to get into a flame war over this topic.
Maybe you should check this out:

http://www.cliftonlaboratories.com/metal_oxide_varistor_(mov).htm

David
did you even READ the wiki article? it appears not.


--
Jim Yanik
jyanik
at
localnet
dot com
 
"David" <someone@somewhere.com> wrote in news:hvlq34$3ic$1@news.eternal-
september.org:

A MOV is somewhat like two back-to-back Zener diodes. It
is
a voltage clamp.

no,it's not. it does not "clamp" the voltage.

You do not pass energy to ground, you pass
current to ground just like you do with any load. The
energy
is totally dissipated in the MOV.
Uh,"passing current to ground" IS passing energy to ground.

David




totally wrong.
Wiki has a nice article on metal-oxide varistor,I suggest
you read it.

--
Jim Yanik
jyanik
at
localnet
dot com

Jim, I am not going to get into a flame war over this topic.
Maybe you should check this out:

http://www.cliftonlaboratories.com/metal_oxide_varistor_(mov).htm

David
http://en.wikipedia.org/wiki/Metal_oxide_varistor

Varistors can absorb part of a surge. How much effect this has on risk to
connected equipment depends on the equipment and details of the selected
varistor. Varistors do not absorb a significant percentage of a lightning
strike, as energy that must be conducted elsewhere is many orders of
magnitude greater than what is absorbed by the small device.

--
Jim Yanik
jyanik
at
localnet
dot com
 
A MOV is somewhat like two back-to-back Zener diodes.
It
is
a voltage clamp.

no,it's not. it does not "clamp" the voltage.

You do not pass energy to ground, you pass
current to ground just like you do with any load. The
energy
is totally dissipated in the MOV.

Uh,"passing current to ground" IS passing energy to
ground.


David




totally wrong.
Wiki has a nice article on metal-oxide varistor,I
suggest
you read it.

--
Jim Yanik
jyanik
at
localnet
dot com

Jim, I am not going to get into a flame war over this
topic.
Maybe you should check this out:

http://www.cliftonlaboratories.com/metal_oxide_varistor_(mov).htm

David



http://en.wikipedia.org/wiki/Metal_oxide_varistor

Varistors can absorb part of a surge. How much effect this
has on risk to
connected equipment depends on the equipment and details
of the selected
varistor. Varistors do not absorb a significant percentage
of a lightning
strike, as energy that must be conducted elsewhere is many
orders of
magnitude greater than what is absorbed by the small
device.

--
Jim Yanik
This is my final say on this topic. In the quote above, you
assume the section saying that "... energy that must be
conducted elsewhere ..." goes to ground through the MOV.
This is where your error resides. The energy is going
elsewhere but being dissipated somewhere else completely
such as blowing up a transformer. The article should also
use the term dissipated elsewhere to make things clearer.

You also assume that passing current is equivalent to
dissipating energy. Current can *move* energy somewhere, but
electrical energy is only dissipated when the current causes
a voltage drop. A perfect ground will not have a voltage
drop so that is not where the the energy is being
dissipated.

David
 