w_tom wrote:
"The guide explains earthing occurs elsewhere."
In the explanation in the IEEE guide "the vast majority of the incoming
lightning surge current flows through the" cable entry ground wire, "and
exits the house via the grounding electrode, as the NEC/CEC writers
intended."
..
"If a power line surge creates a 1,000A current to earth with a very
good resistance to earth of 10 ohms, the power system ground rises
10,000V above 'absolute' earth potential. Much of the effectiveness of
surge protection is keeping the power and phone and cable wires at the
same potential with all of them floating up to 10,000V."
w_ is a fan of ground rods. In general 70% of the voltage drop is in the
first 3 feet from the ground rod. From the ground references (and
wiring)inside the building to earth over 3 feet from the rod there will
be at least 7,000V. A service panel suppressor leaves surge energy still
seeking earth ground.
..
type of surge." SquareD does not even talk about different kinds of
surges. How could your "responsible" company omit this critical information.
Lacking valid technical arguments w_ invents issues.
Plug-in suppressors have MOVs from H-G, N-G, H-N. That is all possible
combinations and all possible surge modes.
In addition, the N-G bond in US services converts common mode power line
surges to transverse mode surges.
--------
Still never seen - a link to another lunatic that agrees with w_ that
plug-in suppressors are NOT effective. Why doesnt anyone agree with you
w_???
Still never answered - embarrassing questions:
- Why do the only 2 examples of protection in the IEEE guide use plug-in
suppressors?
- Why does the NIST guide says plug-in suppressors are "the easiest
solution"?
- How would a service panel suppressor provide any protection in the
IEEE example, pdf page 42?
- Why does the IEEE guide say in the example "the only effective way of
protecting the equipment is to use a multiport protector"?
- Why does SquareD say "electronic equipment may need additional
protection by installing plug-in [suppressors] at the point of use."
- Where is the link to a 75,000A and 1475Joule rated MOV for $0.10.
How can SquareD be a "responsible" company when there is no "spec that
lists each type of surge and protection from that surge".
- Was the UL standard revised as w_'s own hanford link said?
- Did that revision require thermal protection next to the MOVs as w_'s
own hanford link said?
- What was the date of that revision - which w_'s own hanford link said
was UL1449 *2ed*?
- Where specifically in any of w_'s links did anyone say a damaged
suppressor had a UL label?
Where are your answers w_???
For real science read the IEEE and NIST guides. Both say plug-in
suppressors are effective.
--
bud--
Repeating:On Jun 26, 10:07 am, John Fields <jfie...@austininstruments.com
wrote:
You seem to think that someone who can't be afforded whole-house
protection, for whatever reason, should shun the use of plug-in
protectors, even though they have been unequivocally proven to be
effective. Of course, there have been some failures, but that's in
the nature of the game and buying high quality metal-housed units with
high-capacity transient voltage suppressors will go a long way toward
preventing failures.
Clamping two wires together does not dissipate the energy. Surge
energy must be dissipated somewhere.
..
"The guide explains earthing occurs elsewhere."
In the explanation in the IEEE guide "the vast majority of the incoming
lightning surge current flows through the" cable entry ground wire, "and
exits the house via the grounding electrode, as the NEC/CEC writers
intended."
..
Repeating:Clamping the
hot and neutral wire means surge energy remains on both wires -
unclamped - still seeking earth ground.
..
"If a power line surge creates a 1,000A current to earth with a very
good resistance to earth of 10 ohms, the power system ground rises
10,000V above 'absolute' earth potential. Much of the effectiveness of
surge protection is keeping the power and phone and cable wires at the
same potential with all of them floating up to 10,000V."
w_ is a fan of ground rods. In general 70% of the voltage drop is in the
first 3 feet from the ground rod. From the ground references (and
wiring)inside the building to earth over 3 feet from the rod there will
be at least 7,000V. A service panel suppressor leaves surge energy still
seeking earth ground.
..
Neither of the SquareD "whole house" suppressors has numbers for "eachIf plug-in protectors work as you have assumed, then where is this
manufacturer numeric spec that lists each type of surge and protection
from that surge?
..
type of surge." SquareD does not even talk about different kinds of
surges. How could your "responsible" company omit this critical information.
Lacking valid technical arguments w_ invents issues.
Plug-in suppressors have MOVs from H-G, N-G, H-N. That is all possible
combinations and all possible surge modes.
In addition, the N-G bond in US services converts common mode power line
surges to transverse mode surges.
--------
Still never seen - a link to another lunatic that agrees with w_ that
plug-in suppressors are NOT effective. Why doesnt anyone agree with you
w_???
Still never answered - embarrassing questions:
- Why do the only 2 examples of protection in the IEEE guide use plug-in
suppressors?
- Why does the NIST guide says plug-in suppressors are "the easiest
solution"?
- How would a service panel suppressor provide any protection in the
IEEE example, pdf page 42?
- Why does the IEEE guide say in the example "the only effective way of
protecting the equipment is to use a multiport protector"?
- Why does SquareD say "electronic equipment may need additional
protection by installing plug-in [suppressors] at the point of use."
- Where is the link to a 75,000A and 1475Joule rated MOV for $0.10.
How can SquareD be a "responsible" company when there is no "spec that
lists each type of surge and protection from that surge".
- Was the UL standard revised as w_'s own hanford link said?
- Did that revision require thermal protection next to the MOVs as w_'s
own hanford link said?
- What was the date of that revision - which w_'s own hanford link said
was UL1449 *2ed*?
- Where specifically in any of w_'s links did anyone say a damaged
suppressor had a UL label?
Where are your answers w_???
For real science read the IEEE and NIST guides. Both say plug-in
suppressors are effective.
--
bud--