On Sat, 22 Jul 2023 14:21:14 -0700, John Larkin
<jlarkin@highlandSNIPMEtechnology.com> wrote:
In industrial control systems you often use a 6 wire system, three
phases (P1, P2, P3), Neutral (N) Protective Earth (PE) and
Technical/Functional Earth (TE/FE) to carry different kinds of
currents and avoid harmful voltage drops.
The N is polluted by unbalanced single phase loads, especially those
with rectifiers. The N potential in different mains sockets on a site
can be several volts from each other. It is mot a good idea having
some kind of signal ground connection between equipment in two mains
sockets (especially in TN-C systems).
Originally he PE connection was intended to only carry the ground
fault current and reliably blow the fuse. Nowadays the mains EMC
filter capacitors are connected to the PE network, polluting the PE
network with all kinds of high frequency currents, causing
interference voltages between different equipment (even in TN-S).
TE/FE network is supposed not to carry any current and thus no voltage
differences between equipment and hence it can be as a reference for
unbalanced measurement.
Of course this requires that the N, PE and TE/FE networks are kept
separate within the whole industrial site and only connect together
the main busbars together at a single point with heavy jumpers.The
jumpers can be removed during commissioning to verify that N, PE and
TE/FE networks are really separate on the whole site.
Most problems with this system is when local installers note that an
equipment has separate N, PE and TE/FE connections that they are \"at
the sane\" potential and wire then together at the equipment and
connect all to N. :-( You really have to watch what these local
installers are doing.
Fortunately most industrial analog measurements are still 4-20 mA
current loop, which are more or less optoisolated and do not need a
separate ground reference. Signals can be transferred for hundreds of
meters. Serial connections are often optoisolated, Ethernet uses
standard magnetics and optical fibers are used especially in high
interference environments.
One should remember that there is NOT a universal ground potential but
all kinds of (very) local reference potentials at ,ore or less
different potentials..
<jlarkin@highlandSNIPMEtechnology.com> wrote:
I work with one giant organization whose religion includes
single-point grounding not only for multiple boards in a box, but for
entire building-sized systems. That gets absurd. Sometimes their stuff
works, typically after six iterations and three or four years.
In industrial control systems you often use a 6 wire system, three
phases (P1, P2, P3), Neutral (N) Protective Earth (PE) and
Technical/Functional Earth (TE/FE) to carry different kinds of
currents and avoid harmful voltage drops.
The N is polluted by unbalanced single phase loads, especially those
with rectifiers. The N potential in different mains sockets on a site
can be several volts from each other. It is mot a good idea having
some kind of signal ground connection between equipment in two mains
sockets (especially in TN-C systems).
Originally he PE connection was intended to only carry the ground
fault current and reliably blow the fuse. Nowadays the mains EMC
filter capacitors are connected to the PE network, polluting the PE
network with all kinds of high frequency currents, causing
interference voltages between different equipment (even in TN-S).
TE/FE network is supposed not to carry any current and thus no voltage
differences between equipment and hence it can be as a reference for
unbalanced measurement.
Of course this requires that the N, PE and TE/FE networks are kept
separate within the whole industrial site and only connect together
the main busbars together at a single point with heavy jumpers.The
jumpers can be removed during commissioning to verify that N, PE and
TE/FE networks are really separate on the whole site.
Most problems with this system is when local installers note that an
equipment has separate N, PE and TE/FE connections that they are \"at
the sane\" potential and wire then together at the equipment and
connect all to N. :-( You really have to watch what these local
installers are doing.
Fortunately most industrial analog measurements are still 4-20 mA
current loop, which are more or less optoisolated and do not need a
separate ground reference. Signals can be transferred for hundreds of
meters. Serial connections are often optoisolated, Ethernet uses
standard magnetics and optical fibers are used especially in high
interference environments.
One should remember that there is NOT a universal ground potential but
all kinds of (very) local reference potentials at ,ore or less
different potentials..