Instead of rolling blackouts when there\'s a power shortage, why don\'t we just allow (or deliberately) the voltage and frequency to drop? Wouldn\'t that make a lot of devices use less?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Instead of rolling blackouts when there\'s a power shortage, why don\'t we
just allow (or deliberately) the voltage and frequency to drop? Wouldn\'t
that make a lot of devices use less?
\"Commander Kinsey\" <CK1@nospam.com> wrote in message
newsp.1u7t9bhtmvhs6z@ryzen.home...
Instead of rolling blackouts when there\'s a power shortage, why don\'t
we just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
No.
Reducing the frequency will cause mains-referenced clocks to run slow.
And that is many clocks with digital displays (which I thought until
recently used quartz crystals like a watch) and not just older clocks
with synchronous motors. Reducing the frequency too far may affect the
efficiency of transformers: I think reducing the frequency makes it more
likely that the magnetic core will saturate (though I may have got that
the wrong way round!). (*)
Reducing the voltage will reduce the power consumption of resistive
loads such as immersion heaters and cooker hobs/ovens, but may have
little difference to switched-mode power supplies as used in electronic
equipment because they will drawn proportionally more current to
maintain the rated output (eg 5V for phone or 20 V for laptop).
And if the temperature of an oven reduces, or the power output of a
kettle reduces, the appliance will need to be on longer to cook the food
or boil the same amount of water, so there will be no saving. In most
cases you are interested in the transfer of a certain amount of energy
to do a given job, and it doesn\'t matter whether that is transferred as
high power for a small amount of time or a lower power for a longer
period of time.
(*) I\'ve heard it said that transformer-driven devices from the US don\'t
necessarily work efficiently in Europe (even if you correct for the
different voltage) whereas European devices run OK in the US (having
corrected for voltage) because of the difference between 60 Hz (US) and
50 Hz (UK). Or maybe it\'s the opposite way round.
\"Commander Kinsey\" <CK1@nospam.com> wrote in message
newsp.1u7t9bhtmvhs6z@ryzen.home...
Instead of rolling blackouts when there\'s a power shortage, why don\'t
we just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
No.
Reducing the frequency will cause mains-referenced clocks to run slow.
And that is many clocks with digital displays (which I thought until
recently used quartz crystals like a watch) and not just older clocks
with synchronous motors. Reducing the frequency too far may affect the
efficiency of transformers: I think reducing the frequency makes it more
likely that the magnetic core will saturate (though I may have got that
the wrong way round!). (*)
No.
Reducing the frequency will cause mains-referenced clocks to run slow. And
that is many clocks with digital displays (which I thought until recently
used quartz crystals like a watch) and not just older clocks with
synchronous motors. Reducing the frequency too far may affect the efficiency
of transformers: I think reducing the frequency makes it more likely that
the magnetic core will saturate (though I may have got that the wrong way
round!). (*)
Reducing the voltage will reduce the power consumption of resistive loads
such as immersion heaters and cooker hobs/ovens, but may have little
difference to switched-mode power supplies as used in electronic equipment
because they will drawn proportionally more current to maintain the rated
output (eg 5V for phone or 20 V for laptop).
And if the temperature of an oven reduces, or the power output of a kettle
reduces, the appliance will need to be on longer to cook the food or boil
the same amount of water, so there will be no saving. In most cases you are
interested in the transfer of a certain amount of energy to do a given job,
and it doesn\'t matter whether that is transferred as high power for a small
amount of time or a lower power for a longer period of time.
(*) I\'ve heard it said that transformer-driven devices from the US don\'t
necessarily work efficiently in Europe (even if you correct for the
different voltage) whereas European devices run OK in the US (having
corrected for voltage) because of the difference between 60 Hz (US) and 50
Hz (UK). Or maybe it\'s the opposite way round.
Commander Kinsey <CK1@nospam.com> wrote
Instead of rolling blackouts when there\'s a power shortage, why don\'t
we just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
No.
Reducing the frequency too far may affect the efficiency of
transformers: I think reducing the frequency makes it more likely that
the magnetic core will saturate (though I may have got that the wrong
way round!). (*)
(*) I\'ve heard it said that transformer-driven devices from the US don\'t
necessarily work efficiently in Europe (even if you correct for the
different voltage)
whereas European devices run OK in the US (having corrected for voltage)
because of the difference between 60 Hz (US) and 50 Hz (UK).
Or maybe it\'s the opposite way round.
Are you aware that the UK uses 240 Volts instead of 110 Volts in the US? I managed to blow up the SMPS of a large HDD that way.NY <m...@privacy.invalid> wrote
Commander Kinsey <C...@nospam.com> wrote
Instead of rolling blackouts when there\'s a power shortage, why don\'t
we just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
No.
Reducing the frequency too far may affect the efficiency of
transformers: I think reducing the frequency makes it more likely that
the magnetic core will saturate (though I may have got that the wrong
way round!). (*)
(*) I\'ve heard it said that transformer-driven devices from the US don\'t
necessarily work efficiently in Europe (even if you correct for the
different voltage)
We had a brand new US manufactured mass spectrometer quite
literally catch fire because it didnt like running on 50Hz instead
of 60Hz. The main transformer overheated and caught fire.
whereas European devices run OK in the US (having corrected for voltage)
because of the difference between 60 Hz (US) and 50 Hz (UK).
Or maybe it\'s the opposite way round.
Nope, you have it the right way round.
On Monday, 7 November 2022 at 17:58:15 UTC, Rod Speed wrote:
NY <m...@privacy.invalid> wrote
Commander Kinsey <C...@nospam.com> wrote
Instead of rolling blackouts when there\'s a power shortage, why don\'t
we just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
No.
Reducing the frequency too far may affect the efficiency of
transformers: I think reducing the frequency makes it more likely that
the magnetic core will saturate (though I may have got that the wrong
way round!). (*)
(*) I\'ve heard it said that transformer-driven devices from the US don\'t
necessarily work efficiently in Europe (even if you correct for the
different voltage)
We had a brand new US manufactured mass spectrometer quite
literally catch fire because it didnt like running on 50Hz instead
of 60Hz. The main transformer overheated and caught fire.
whereas European devices run OK in the US (having corrected for voltage)
because of the difference between 60 Hz (US) and 50 Hz (UK).
Or maybe it\'s the opposite way round.
Nope, you have it the right way round.
Are you aware that the UK uses 240 Volts instead of 110 Volts in the US? I managed to blow up the SMPS of a large HDD that way.
Wim
On 07/11/2022 14:45, NY wrote:
\"Commander Kinsey\" <CK1@nospam.com> wrote in message
newsp.1u7t9bhtmvhs6z@ryzen.home...
Instead of rolling blackouts when there\'s a power shortage, why don\'t
we just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
No.
Reducing the frequency will cause mains-referenced clocks to run slow.
And that is many clocks with digital displays (which I thought until
recently used quartz crystals like a watch) and not just older clocks
with synchronous motors. Reducing the frequency too far may affect the
efficiency of transformers: I think reducing the frequency makes it more
likely that the magnetic core will saturate (though I may have got that
the wrong way round!). (*)
No, you\'re spot on. It has been discussed in this group before. In
general, 60Hz transformers can either be more efficient or smaller than
their 50Hz cousins.
On 07/11/2022 14:45, NY wrote:
\"Commander Kinsey\" <CK1@nospam.com> wrote in message
newsp.1u7t9bhtmvhs6z@ryzen.home...
Instead of rolling blackouts when there\'s a power shortage, why don\'t
we just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
No.
Reducing the frequency will cause mains-referenced clocks to run slow.
And that is many clocks with digital displays (which I thought until
recently used quartz crystals like a watch) and not just older clocks
with synchronous motors. Reducing the frequency too far may affect the
efficiency of transformers: I think reducing the frequency makes it more
likely that the magnetic core will saturate (though I may have got that
the wrong way round!). (*)
No, you\'re spot on. It has been discussed in this group before. In
general, 60Hz transformers can either be more efficient or smaller than
their 50Hz cousins.
It is a legal requirement to keep the frequency at 50Hz over a set period.
Therefore if it lags at any point they have to increase to catch up.
This was a legal requirement due to mains clocks.
On 2022-11-09 20:55, Commander Kinsey wrote:
On Wed, 09 Nov 2022 19:48:27 -0000, Carlos E.R.
robin_listas@es.invalid> wrote:
On 2022-11-09 20:10, Commander Kinsey wrote:
On Wed, 09 Nov 2022 16:07:42 -0000, Anthony Stewart
tony.sunnysky@gmail.com> wrote:
On Sunday, 6 November 2022 at 09:23:34 UTC-5, Commander Kinsey wrote:
Instead of rolling blackouts when there\'s a power shortage, why don\'t
we just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
Most loads are energy-based with negative feedback (anything with a
sensor like a thermostat) and not power-based. The countries like
Indo-Paki have always lived with brownouts which stimulated mass-sale
of \"voltage stabilizers\" which are negative incremental impedance
converters that cumulatively adds more instability.
As local demand current increases from voltage reduction and
tap-change to increase the voltage which causes more current and
voltage drop when accumulated by many users of further reduces
disti-load voltage, leading to unstable frequent daily blackouts.
So end-users of stabilizers increase grid instability.
Current (pun intended) customer outages are:
USA 60k (s. east+west coast)
Canada 14k
UK 1.5k
UA massive outage from RU destruction
Are you sure they cause instability? They don\'t increase the power
used, they increase the current to compensate for the voltage drop.
Instability would only occur if the generators stalled, which happens if
the power drawn exceeds what they can provide. If they\'re anything like
a car alternator, the same power can come out at any revs.
Think.
The generator(s) can not cope with the load, so the voltage drops. The
stabilizers at the clients rise the current and keep the power constant,
instead of decreasing, causing the generators to drop speed instead
(because they can not cope). Normally, when the speed drops below a
value, the generator disconnects. Cascade failure. General blackout,
unless some areas disconnect from the too loaded areas and isolate.
I was assuming a voltage drop caused on purpose later on, not at the
generator. I was originally asking about reducing peak usage problems
for short periods. The electric company could drop a winding or two
somewhere to lower everyone\'s voltage. So resistive loads would use
less, and loads you\'re talking about would use precisely the same (as
far as the generator is concerned, as it\'s output voltage and current
remain the same).
Hum.
Dunno.
Maybe.
But if this strategy \"works\", the current increase causes more stress on
the hardware: it heats more. Maybe destructively.
On 11/9/2022 11:48 AM, Carlos E.R. wrote:
On 2022-11-09 20:10, Commander Kinsey wrote:
On Wed, 09 Nov 2022 16:07:42 -0000, Anthony Stewart
tony.sunnysky@gmail.com> wrote:
On Sunday, 6 November 2022 at 09:23:34 UTC-5, Commander Kinsey wrote:
Instead of rolling blackouts when there\'s a power shortage, why
don\'t we just allow (or deliberately) the voltage and frequency to
drop? Wouldn\'t that make a lot of devices use less?
Most loads are energy-based with negative feedback (anything with a
sensor like a thermostat) and not power-based. The countries like
Indo-Paki have always lived with brownouts which stimulated mass-sale
of \"voltage stabilizers\" which are negative incremental impedance
converters that cumulatively adds more instability.
As local demand current increases from voltage reduction and
tap-change to increase the voltage which causes more current and
voltage drop when accumulated by many users of further reduces
disti-load voltage, leading to unstable frequent daily blackouts.
So end-users of stabilizers increase grid instability.
Current (pun intended) customer outages are:
USA 60k (s. east+west coast)
Canada 14k
UK 1.5k
UA massive outage from RU destruction
Are you sure they cause instability? They don\'t increase the power
used, they increase the current to compensate for the voltage drop.
Instability would only occur if the generators stalled, which happens
if the power drawn exceeds what they can provide. If they\'re anything
like a car alternator, the same power can come out at any revs.
Think.
The generator(s) can not cope with the load, so the voltage drops. The
stabilizers at the clients rise the current and keep the power constant,
instead of decreasing, causing the generators to drop speed instead
(because they can not cope). Normally, when the speed drops below a
value, the generator disconnects. Cascade failure. General blackout,
unless some areas disconnect from the too loaded areas and isolate.
If different generators get out of sync, everything craps out, as the
current tries to correct that. Huge currents and forces can result,
destroying equipment. Keeping the sources of power in sync is probably
one of the most important constraints of running the power networks.
\"Synchronizing a generator to the power system must be
done carefully. The speed (frequency) and voltage of the
isolated generator must be closely matched, and the rotor
angle must be close to the instantaneous power system phase
angle prior to closing the generator breaker to connect the
isolated generator to the power system. Poor synchronizing
can:
⢠Damage the generator and the prime mover because of
mechanical stresses caused by rapid acceleration or
deceleration, bringing the rotating masses into
synchronism (exactly matched speed and rotor angle)
with the power system.
⢠Damage the generator and step-up transformer
windings caused by high currents.
⢠Cause disturbances to the power system such as power
oscillations and voltage deviations from nominal.
⢠Prevent the generator from staying online and picking
up load when protective relay elements interpret the
condition as an abnormal operating condition and trip
the generator\"
https://cms-cdn.selinc.com/assets/Literature/Publications/Technical%20Papers/6459_FundamentalsAdvancements_MT_20120402_Web2.pdf?v=20191007-203006#:~:text=Poor%20synchronizing%20can%3A&text=Damage%20the%20generator%20and%20the,angle)%20with%20the%20power%20system.
On 2022-11-12 15:17, Commander Kinsey wrote:
On Sat, 12 Nov 2022 13:39:00 -0000, Carlos E.R.
robin_listas@es.invalid> wrote:
On 2022-11-12 14:22, Commander Kinsey wrote:
On Fri, 11 Nov 2022 17:55:38 -0000, rick
rick_hughes@_remove_btconnect.com> wrote:
On 06/11/2022 14:23, Commander Kinsey wrote:
Instead of rolling blackouts when there\'s a power shortage, why
don\'t we
just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
It is a legal requirement to keep the frequency at 50Hz over a set
period.
Therefore if it lags at any point they have to increase to catch up.
This was a legal requirement due to mains clocks.
But you can drop it to 49 for a while then put it up to 51 when there\'s
plenty power.
And do it in the entire Europe, simultaneously?
We\'re linked by DC, so no.
Wrong.
On Sat, 12 Nov 2022 08:43:56 -0500, hubops@ccanoemail.com wrote:
System frequency is maintained within very tight tolerances -
- for a variety of reasons. Large thermal generators are quite
fussy about frequency.
Big generators are synchronous generators and the question is how do
you connect a large number in parallel (in the national grid) and how
properly share the generated power between them. The power delivered
depends on the _phase_difference_ between generators i.e. a constant
phase difference.
[...]
That can in fact be done. And was done. And it wrecked equipment inOn 2022-11-12 14:22, Commander Kinsey wrote:
On Fri, 11 Nov 2022 17:55:38 -0000, rick
rick_hughes@_remove_btconnect.com> wrote:
On 06/11/2022 14:23, Commander Kinsey wrote:
Instead of rolling blackouts when there\'s a power shortage, why
don\'t we
just allow (or deliberately) the voltage and frequency to drop?
Wouldn\'t that make a lot of devices use less?
It is a legal requirement to keep the frequency at 50Hz over a set
period.
Therefore if it lags at any point they have to increase to catch up.
This was a legal requirement due to mains clocks.
But you can drop it to 49 for a while then put it up to 51 when
there\'s plenty power.
And do it in the entire Europe, simultaneously?