fredag den 8. september 2023 kl. 19.54.14 UTC+2 skrev Ricky:
afaik the big overhead lines are usually aluminium, https://en.wikipedia.org/wiki/Aluminium-conductor_steel-reinforced_cable
On Friday, September 8, 2023 at 12:38:54â¯PM UTC-4, Ralph Mowery wrote:
In article <33dmfi5fh5t6l10jm...@4ax.com>,
upsid...@downunder.com says...
A 1 m long 1 mm2 copper wire has a resistance of 17 mOhm, thus 1 km
has 17 ohm resistance and the total loop resistance 4500 km (x2) cable
is 150 kOhm. Running the ordinary 1 A/mm2 current density through the
loop and 150 KV is lost. Using 0,5 A/mm2 current density the total
voltage loss will drop to 75 kV, which would be bearable for a 1000 kV
system.
If you would like to run 1 GW through the system, the current needs to
be 1000 A, so each cable needs to have a 2000 mm2 cross section at 0.5
A/mm2 (50 mm diameter)
The copper density is 9 kg/dm3 thus 18 kg/m or 160000 toms for the
whole system. Assuming 5 euros/kg, the total cost of raw copper would
be 800 million euros. Making HV cables of it would multiply the price
several times.
There is a lot off math involved there.
I do not know how it will change things but if 60 HZ or some other AC
frequency is used on very long wires the lines act like a radio
frequency transmission line and other factors may need to be added in.
It\'s not that the wires become radio antenna. Rather there is an effect called the skin effect, where the current is concentrated near the surface of the conductor. The work around, is to split the single fat cable into multiple smaller diameter cables. If you look at high voltage power lines, you will often see each of the three phase conductors spread by triangular spacers with three wires. The three smaller wires carry more current than a single wire with the same copper, because of the skin effect.
afaik the big overhead lines are usually aluminium, https://en.wikipedia.org/wiki/Aluminium-conductor_steel-reinforced_cable