On Aug 8, 10:50 am, "Jon" <jon8...@peoplepc.com> wrote:
The electrical service goes to the house. There are 3 underground 000
cables that go to the barn from the house. The barn has a 60 amp breaker
in
the breaker box at the house. The 12,000 watt generator is in the barn. It
has a 50 amp 240vac outlet, a 30 amp 240vac outlet and several others. I
am
hooking the 50 amp outlet to the house. I am using the same 3 underground
000 cables to send generator power to the house during a power outage.

A 90 amp contactor in the barn won't connect the generator to the house
unless:
1. The electrical service to the house is off, and
2. The service disconnect switch at the house is off.

When the generator is turned on, it tests the service disconnect at the
house to assure the above two conditions are met. This is done by sending
a
1 second electrical pulse to the house to see if it will actuate a coil.
If
the coil actuates, the 90 amp contactor latches open and prevents backfeed
into the grid. If the service power turns on during that 1 second, the
generator power and service power will clash and throw a 50 amp breaker to
the generator.

http://jons-math.bravehost.com/transfer.html
Jon
You appear to have two control conductors going to the house panel
that are not the AWG 0 cables that you mentioned. Is that correct?
If it is you can fix this setup by using a shunt trip main breaker
with a pair of auxiliary contacts. If you actually interested in
anything other than trying to validate your existing setup let me
know.
--
Tom Horne


You too, another sick circuit designer...Heehee.......
 
"PeterD" <peter2@hipson.net> wrote in message
news:2quv5690dn5n8emohuv1smarrofoehivv2@4ax.com...
On 9 Aug 2010 11:02:02 GMT, Jasen Betts <jasen@xnet.co.nz> wrote:

On 2010-08-08, Jon <jon8338@peoplepc.com> wrote:

If the service power turns on during that 1 second, the
generator power and service power will clash and throw a 50 amp breaker
to
the generator.

if you're lucky.


Actually it'll probably blow his generator, and resolve the problem
almost immediately... With luck, Jon will be fondleing it at the time.
10 points to you..
 
"Jon" <jon8338@peoplepc.com> wrote in message
news:4YqdnV_GCaqgWcPRnZ2dnUVZ_gudnZ2d@earthlink.com...
The electrical service goes to the house. There are 3 underground 000
cables that go to the barn from the house. The barn has a 60 amp breaker
in the breaker box at the house. The 12,000 watt generator is in the
barn. It has a 50 amp 240vac outlet, a 30 amp 240vac outlet and several
others. I am hooking the 50 amp outlet to the house. I am using the same
3 underground 000 cables to send generator power to the house during a
power outage.

A 90 amp contactor in the barn won't connect the generator to the house
unless:
1. The electrical service to the house is off, and
2. The service disconnect switch at the house is off.

When the generator is turned on, it tests the service disconnect at the
house to assure the above two conditions are met. This is done by sending
a 1 second electrical pulse to the house to see if it will actuate a coil.
If the coil actuates, the 90 amp contactor latches open and prevents
backfeed into the grid. If the service power turns on during that 1
second, the generator power and service power will clash and throw a 50
amp breaker to the generator.

http://jons-math.bravehost.com/transfer.html
 
On Aug 11, 9:23 pm, "Very Sick Edmond Wollmann"
<arcturian...@earthlink.net> wrote:

SOME WHINEY PINEY CRAP NIOT ORTH QUOTING

THIS ISN'T MAMBY PAMBY LAND!
IF YOU ARE GOING TO CHANGE THE TOPIC NAME
WATCH YOUR SICK DUMBASS WORDING

THERE ARE CHILDREN WATCHING
AND THERE ARE NO CHILD GUARDS IN PALCE HERE KLEDMOND

CONTROL YOURSELF

IAP
 
"Retarded Proteus IIV" <proteusiiv@gmail.com> wrote his non-sense
news:f67bb64d-3ed9-4477-9a9d-0b5bff1de051@5g2000yqz.googlegroups.com...
On Aug 11, 9:23 pm, "Very Sick Edmond Wollmann"
<arcturian...@earthlink.net> wrote:

SOME WHINEY PINEY CRAP NIOT ORTH QUOTING

THIS ISN'T MAMBY PAMBY LAND!
IF YOU ARE GOING TO CHANGE THE TOPIC NAME
WATCH YOUR SICK DUMBASS WORDING

THERE ARE CHILDREN WATCHING
AND THERE ARE NO CHILD GUARDS IN PALCE HERE KLEDMOND

CONTROL MESELF

IAP
 
"Proteus IIV" <proteusiiv@gmail.com> wrote in message
news:f67bb64d-3ed9-4477-9a9d-0b5bff1de051@5g2000yqz.googlegroups.com...
On Aug 11, 9:23 pm, "Very Sick Edmond Wollmann"
<arcturian...@earthlink.net> wrote:

SOME WHINEY PINEY CRAP NIOT ORTH QUOTING

THIS ISN'T MAMBY PAMBY LAND!
IF YOU ARE GOING TO CHANGE THE TOPIC NAME
WATCH YOUR SICK DUMBASS WORDING

THERE ARE CHILDREN WATCHING
AND THERE ARE NO CHILD GUARDS IN PALCE HERE KLEDMOND

CONTROL YOURSELF

IAP
 
On 9/08/2010 12:50 AM, Jon wrote:
The electrical service goes to the house. There are 3 underground 000
cables that go to the barn from the house. The barn has a 60 amp breaker
in the breaker box at the house. The 12,000 watt generator is in the
barn. It has a 50 amp 240vac outlet, a 30 amp 240vac outlet and several
others. I am hooking the 50 amp outlet to the house. I am using the same
3 underground 000 cables to send generator power to the house during a
power outage.

A 90 amp contactor in the barn won't connect the generator to the house
unless:
1. The electrical service to the house is off, and
2. The service disconnect switch at the house is off.

When the generator is turned on, it tests the service disconnect at the
house to assure the above two conditions are met. This is done by
sending a 1 second electrical pulse to the house to see if it will
actuate a coil. If the coil actuates, the 90 amp contactor latches open
and prevents backfeed into the grid. If the service power turns on
during that 1 second, the generator power and service power will clash
and throw a 50 amp breaker to the generator.

http://jons-math.bravehost.com/transfer.html
I'd have thought the grid operator would want a cast-iron guarantee that
you won't backfeed the grid, lest you enliven wires that linesmen think
are dead.

What's wrong with a DPDT relay?

Sylvia.
 
"Sylvia Else" <sylvia@not.here.invalid> wrote in message
news:8chtp7FjduU1@mid.individual.net...
On 9/08/2010 12:50 AM, Jon wrote:
The electrical service goes to the house. There are 3 underground 000
cables that go to the barn from the house. The barn has a 60 amp breaker
in the breaker box at the house. The 12,000 watt generator is in the
barn. It has a 50 amp 240vac outlet, a 30 amp 240vac outlet and several
others. I am hooking the 50 amp outlet to the house. I am using the same
3 underground 000 cables to send generator power to the house during a
power outage.

A 90 amp contactor in the barn won't connect the generator to the house
unless:
1. The electrical service to the house is off, and
2. The service disconnect switch at the house is off.

When the generator is turned on, it tests the service disconnect at the
house to assure the above two conditions are met. This is done by
sending a 1 second electrical pulse to the house to see if it will
actuate a coil. If the coil actuates, the 90 amp contactor latches open
and prevents backfeed into the grid. If the service power turns on
during that 1 second, the generator power and service power will clash
and throw a 50 amp breaker to the generator.

http://jons-math.bravehost.com/transfer.html




I'd have thought the grid operator would want a cast-iron guarantee that
you won't backfeed the grid, lest you enliven wires that linesmen think
are dead.

What's wrong with a DPDT relay?

Sylvia.
He can't back-feed to the grid any way pussy, The grid power is so much
powerful than his funky generator, it will smoke first or nothing will
happen depending on the polarity of the flow.
 
On 12/08/2010 7:45 PM, Very Sick Edmond Wollmann wrote:
"Sylvia Else" <sylvia@not.here.invalid> wrote in message
news:8chtp7FjduU1@mid.individual.net...
On 9/08/2010 12:50 AM, Jon wrote:
The electrical service goes to the house. There are 3 underground 000
cables that go to the barn from the house. The barn has a 60 amp breaker
in the breaker box at the house. The 12,000 watt generator is in the
barn. It has a 50 amp 240vac outlet, a 30 amp 240vac outlet and several
others. I am hooking the 50 amp outlet to the house. I am using the same
3 underground 000 cables to send generator power to the house during a
power outage.

A 90 amp contactor in the barn won't connect the generator to the house
unless:
1. The electrical service to the house is off, and
2. The service disconnect switch at the house is off.

When the generator is turned on, it tests the service disconnect at the
house to assure the above two conditions are met. This is done by
sending a 1 second electrical pulse to the house to see if it will
actuate a coil. If the coil actuates, the 90 amp contactor latches open
and prevents backfeed into the grid. If the service power turns on
during that 1 second, the generator power and service power will clash
and throw a 50 amp breaker to the generator.

http://jons-math.bravehost.com/transfer.html




I'd have thought the grid operator would want a cast-iron guarantee
that you won't backfeed the grid, lest you enliven wires that linesmen
think are dead.

What's wrong with a DPDT relay?

Sylvia.

He can't back-feed to the grid any way pussy, The grid power is so much
powerful than his funky generator, it will smoke first or nothing will
happen depending on the polarity of the flow.
That's true if the lines he's feeding are actually connected to the
grid. The problem arises when they're disconnected at some other point
so that they can be worked on. If he backfeeds them then, he can
electrocute someone.

Sylvia.
 
"Sylvia Else" <sylvia@not.here.invalid> wrote in message
news:8chuh1FonqU1@mid.individual.net...
On 12/08/2010 7:45 PM, Very Sick Edmond Wollmann wrote:

"Sylvia Else" <sylvia@not.here.invalid> wrote in message
news:8chtp7FjduU1@mid.individual.net...
On 9/08/2010 12:50 AM, Jon wrote:
The electrical service goes to the house. There are 3 underground 000
cables that go to the barn from the house. The barn has a 60 amp
breaker
in the breaker box at the house. The 12,000 watt generator is in the
barn. It has a 50 amp 240vac outlet, a 30 amp 240vac outlet and several
others. I am hooking the 50 amp outlet to the house. I am using the
same
3 underground 000 cables to send generator power to the house during a
power outage.

A 90 amp contactor in the barn won't connect the generator to the house
unless:
1. The electrical service to the house is off, and
2. The service disconnect switch at the house is off.

When the generator is turned on, it tests the service disconnect at the
house to assure the above two conditions are met. This is done by
sending a 1 second electrical pulse to the house to see if it will
actuate a coil. If the coil actuates, the 90 amp contactor latches open
and prevents backfeed into the grid. If the service power turns on
during that 1 second, the generator power and service power will clash
and throw a 50 amp breaker to the generator.

http://jons-math.bravehost.com/transfer.html




I'd have thought the grid operator would want a cast-iron guarantee
that you won't backfeed the grid, lest you enliven wires that linesmen
think are dead.

What's wrong with a DPDT relay?

Sylvia.

He can't back-feed to the grid any way pussy, The grid power is so much
powerful than his funky generator, it will smoke first or nothing will
happen depending on the polarity of the flow.


That's true if the lines he's feeding are actually connected to the grid.
The problem arises when they're disconnected at some other point so that
they can be worked on. If he backfeeds them then, he can electrocute
someone.

Sylvia.
True, but he tried not to do that, that's why he struggled with his transfer
circuit.
 
On 2010-08-09, PeterD <peter2@hipson.net> wrote:
On 9 Aug 2010 11:02:02 GMT, Jasen Betts <jasen@xnet.co.nz> wrote:

On 2010-08-08, Jon <jon8338@peoplepc.com> wrote:

If the service power turns on during that 1 second, the
generator power and service power will clash and throw a 50 amp breaker to
the generator.

if you're lucky.


Actually it'll probably blow his generator, and resolve the problem
almost immediately... With luck, Jon will be fondleing it at the time.
that's now way it could go, another is the gernerator could phase-lock
with the mains. and continue to run.



--- news://freenews.netfront.net/ - complaints: news@netfront.net ---
 
On Thu, 12 Aug 2010 02:45:52 -0700, "Very Sick Edmond Wollmann"
<arcturianone@earthlink.net> wrote:

...

He can't back-feed to the grid any way pussy, The grid power is so much
powerful than his funky generator, it will smoke first or nothing will
happen depending on the polarity of the flow.
Yes, he can. If the grid is open, and the lineman is trying to repair
that open, there is a (high) risk of voltage.
 
On Thu, 12 Aug 2010 03:01:28 -0700, "Very Sick Edmond Wollmann"
<arcturianone@earthlink.net> wrote:


True, but he tried not to do that, that's why he struggled with his transfer
circuit.
Again this makes too many hazardous assumptions about conditions and
Jon's ability to do things. Since he's proven he can not design a
simple transfer switch, there is little hope that he will have ideal
conditions for his system to work.

One problem is that Jon engineers for best/ideal conditions, and not
worst case conditions. That is what seperates a real engineer from a
wanna-be like Jon.
 
Sylvia Else wrote:
On 9/08/2010 12:50 AM, Jon wrote:
The electrical service goes to the house. There are 3 underground 000
cables that go to the barn from the house. The barn has a 60 amp breaker
in the breaker box at the house. The 12,000 watt generator is in the
barn. It has a 50 amp 240vac outlet, a 30 amp 240vac outlet and several
others. I am hooking the 50 amp outlet to the house. I am using the same
3 underground 000 cables to send generator power to the house during a
power outage.

A 90 amp contactor in the barn won't connect the generator to the house
unless:
1. The electrical service to the house is off, and
2. The service disconnect switch at the house is off.

When the generator is turned on, it tests the service disconnect at the
house to assure the above two conditions are met. This is done by
sending a 1 second electrical pulse to the house to see if it will
actuate a coil. If the coil actuates, the 90 amp contactor latches open
and prevents backfeed into the grid. If the service power turns on
during that 1 second, the generator power and service power will clash
and throw a 50 amp breaker to the generator.

http://jons-math.bravehost.com/transfer.html




I'd have thought the grid operator would want a cast-iron guarantee that
you won't backfeed the grid, lest you enliven wires that linesmen think
are dead.

What's wrong with a DPDT relay?

Jon is a troll.
 
Psychiatric medication...
http://en.wikipedia.org/wiki/Psychiatric_medication
 
On Aug 12, 12:39 pm, "Bill" <billnomailnosp...@yahoo.com> wrote:
Psychiatric medication...http://en.wikipedia.org/wiki/Psychiatric_medication
BILL
IF YOU ARE RESTLESS AND NEED TO BE DOING SOMETHING WITH YOUR HANDS
AS GOOD AS THOSE MEDICATIONNS MAY BE [I WOULD SUGGEST YOU TAKE THE
ANTI-ANXIETY PILLS]
INSTEAD GO BUY A "FUSHIGI" AS SEN ON TV
AND STAY OFF YOUR KEYBORAD

IAP
 
We don't care about your communication failures.

"Michael A. Terrell" <mike.terrell@earthlink.net> wrote in message
news:YuSdnQXFp-ixvvnRnZ2dnUVZ_rCdnZ2d@earthlink.com...
Jon is a troll.
 
Josepi wrote:
We don't care about your communication failures.

You seem to be the one who can't communicate, but I really don't
care.
 
"Bill" <billnomailnospamx@yahoo.com> wrote in message
news:8cime6Fa0nU1@mid.individual.net...
Psychiatric medication...
http://en.wikipedia.org/wiki/Psychiatric_medication
Psychiatric Rethinking needed for your Superpower Krooks.

After you failed to robbed IRAQ, now you robbed your own people, stealing
their houses on a GRAND THEFT scheme, banks changing the rule to rob,
bail-out money went to the wrong hands....

I call this a Karma of Ignorants.
 
"Michael A. Terrell" <mike.terrell@earthlink.net> wrote in message
news:W_WdnWc1Lo5bcfnRnZ2dnUVZ_tmdnZ2d@earthlink.com...
Josepi wrote:

We don't care about your communication failures.


You seem to be the one who can't communicate, but I really don't
care.
Actually you are the one Michael Asshole Terrell.

Jon tried his best, you don't have experience as much as he does in high
power, he did 95% right, so, you're a military Junk. If you think you're
smart, why didn't you help him?
 