w_tom wrote:
The 2nd TV suffers 8,000V because a surge comes in on a cable service.
Without a surge suppressor at the TV1 the voltage would have been
10,000V. The suppressor at TV1 causes no damage to TV2.
The point of the illustration for the IEEE, and anyone who can think, is
"to protect TV2, a second multiport protector located at TV2 is required."
w_ says suppressors must only be at the service panel. In this example a
service panel protector would provide absolutely *NO* protection. The
problem is the wire connecting the cable entry block to the power
service 'ground' is too long (a common problem). The IEEE guide says in
that case "the only effective way of protecting the equipment is to use
a multiport [plug-in] protector."
Grounding Sensitive Electronic Equipment"), an IEEE standard, recognizes
plug-in suppressors as an effective protection device.
earthing. The question is whether plug-in suppressors work. Both the
IEEE and NIST guides say plug-in suppressors are effective. So does
sparkys quote from the Federal Citizen Information Center.
In answer to the OP - look at the 2 examples of surge protection in the
IEEE guide. One of them is for a TV and related equipment and uses a
plug-in suppressor.
Still never seen - a source that agrees with w_ that plug-in suppressors
do NOT work.
Still never answered - embarrassing questions:
- Why do the only 2 examples of protection in the IEEE guide use plug-in
suppressors?
- Why does the NIST guide says plug-in suppressors are "the easiest
solution"?
--
bud--
The lie repeated.On May 25, 2:00 pm, sparky <sparky...@yahoo.com> wrote:
Not all equipment comes with a grouded cord. Plugin protectors will
protect this equipment equally as well as a groundedprotector.
The protection will be almost as good as a whole houseprotector.
Plug-in protectors can even contribute to damage of the adjacent
appliance. That is the point of a Bud citation - Page 42 Figure 8.
The adjacent TV (even a two wire TV) suffered 8000 volts because the
nearby plug-in protector earthed that surge through the TV.
The 2nd TV suffers 8,000V because a surge comes in on a cable service.
Without a surge suppressor at the TV1 the voltage would have been
10,000V. The suppressor at TV1 causes no damage to TV2.
The point of the illustration for the IEEE, and anyone who can think, is
"to protect TV2, a second multiport protector located at TV2 is required."
w_ says suppressors must only be at the service panel. In this example a
service panel protector would provide absolutely *NO* protection. The
problem is the wire connecting the cable entry block to the power
service 'ground' is too long (a common problem). The IEEE guide says in
that case "the only effective way of protecting the equipment is to use
a multiport [plug-in] protector."
The IEEE Emerald book ("IEEE Recommended Practice for Powering andIEEE Green Book puts numbers
Grounding Sensitive Electronic Equipment"), an IEEE standard, recognizes
plug-in suppressors as an effective protection device.
The required statement of religious belief in earthing. Everyone is forA protector is only as effective as its earth ground. No earth
ground (ie plug-in protectors) means no effective protection.
earthing. The question is whether plug-in suppressors work. Both the
IEEE and NIST guides say plug-in suppressors are effective. So does
sparkys quote from the Federal Citizen Information Center.
In answer to the OP - look at the 2 examples of surge protection in the
IEEE guide. One of them is for a TV and related equipment and uses a
plug-in suppressor.
Still never seen - a source that agrees with w_ that plug-in suppressors
do NOT work.
Still never answered - embarrassing questions:
- Why do the only 2 examples of protection in the IEEE guide use plug-in
suppressors?
- Why does the NIST guide says plug-in suppressors are "the easiest
solution"?
--
bud--