** In any case, the only time the neutral can be left floating in when the
3 phase load is ONE device.
Where multiple, single phase devices constitute the total load, each with
thier own switches, fuses etc it is utterly out of the question.
........... Phil
"FruitLoop" <Hyperactive@fruitloop.net
** The excess neutral current will be a major problem.
Thats bullshit , if the 3 phase load is close to balanced then the
neutral
technically can be floating .
Phil's post seems valid to me.
This article mentions the non-balanced neutral problem.
http://www.jmwa.demon.co.uk/EMCLF0010.htm
3 phase balancing works when the loads draw sinusoidal current. Computer
monitors have bridge rectifiers across the mains input, which charge
capacitors with short pulses of current near the peaks of the sinewave. So
the phases see large amplitude, narrow current pulses - at 120 degree
timing
with little neutral cancellation - so the neutral wire is working very
hard.
** In any case, the only time the neutral can be left floating in when the
3 phase load is ONE device.
Where multiple, single phase devices constitute the total load, each with
thier own switches, fuses etc it is utterly out of the question.
........... Phil