On Tue, 10 May 2005 09:25:05 +0100, Tony Williams
<tonyw@ledelec.demon.co.uk> put finger to keyboard and composed:
7.6mAmpere.Turns. This in turn suggests that a perfectly balanced load
current of 100A is creating a core imbalance equivalent to that
expected for a leakage current of 7.6mA. I wonder if you now pass a
single wire through the core whether an ammeter will measure 7.6mA.
- Franc Zabkar
--
Please remove one 's' from my address when replying by email.
<tonyw@ledelec.demon.co.uk> put finger to keyboard and composed:
Hmmm, that means there must be a net flux equivalent toIn article <m7mv711o7d1optojtlsk2del9d5qsnih9a@4ax.com>,
Franc Zabkar <fzabkar@optussnet.com.au> wrote:
Unfortunately I don't have access to a meter, so I am unable to
test my idea.
I still have some CT test kit still around,
and it is a trivial experiment to do, as below.
The CT has a 1000 turn secondary and I still have
an old 100-way plug+socket arrangement, with 100
wires, arranged as 50+50 turns. So those 50+50
turns can be the primary, wired either as series-
-adding or series-opposing. A primary current
of 1A is equivalent to 100A in a bar-primary.
Here are the results.
2. Series-opposing 50-50 turn pri, 1000 turn sec.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
2a. Straight through, return bundle as far away as poss.
Ipri= 1.020A, Isec= 7.6uA.... yes, microamps.
7.6mAmpere.Turns. This in turn suggests that a perfectly balanced load
current of 100A is creating a core imbalance equivalent to that
expected for a leakage current of 7.6mA. I wonder if you now pass a
single wire through the core whether an ammeter will measure 7.6mA.
- Franc Zabkar
--