We recently caught a purchasing error in production. 300V wire was
accidently purchased instead of the specified 600V rated wire. This
wire is used to connect a 3 phase 480V motor to a combination starter.
After this occurred I tried to figure worst case scenario but am having
trouble. If a single line voltage is 277 to neutral, is the 300 volt
wire okay in this case?
If line to line is 480V, wouldn't two 300V wires really be 600V
protection from conductor to insulator (for line 1) to insulator to
conductor (for line 2)?