Wire size question

Guest
Hi,
If I have a 10 hp, 230 vac, 3ph motor with a current draw of 24 amps.
I would fuse it with a 30 amp time delay.

OK now my question. Do I wire it with the capability of handling 24
amps or 30 amps?

Thanks for the help.
 
somewere@out.there wrote:

Hi,
If I have a 10 hp, 230 vac, 3ph motor with a current draw of 24 amps.
I would fuse it with a 30 amp time delay.

OK now my question. Do I wire it with the capability of handling 24
amps or 30 amps?

Thanks for the help.
you calculate 25% over the Max expected current.
so,
24 * 1.25 = 30 amps

Is the minimum to start with, then you have length of
wire to consider.

--
"I'd rather have a bottle in front of me than a frontal lobotomy"
http://webpages.charter.net/jamie_5
 
On Wed, 05 Dec 2007 21:12:06 -0500, somewere@out.there wrote:

Hi,
If I have a 10 hp, 230 vac, 3ph motor with a current draw of 24 amps.
I would fuse it with a 30 amp time delay.

OK now my question. Do I wire it with the capability of handling 24
amps or 30 amps?

Thanks for the help.
How long is the wire?
 
On Thu, 06 Dec 2007 10:56:54 -0500, PeterD <peter2@hipson.net> wrote:

On Wed, 05 Dec 2007 21:12:06 -0500, somewere@out.there wrote:

Hi,
If I have a 10 hp, 230 vac, 3ph motor with a current draw of 24 amps.
I would fuse it with a 30 amp time delay.

OK now my question. Do I wire it with the capability of handling 24
amps or 30 amps?

Thanks for the help.

How long is the wire?
It's nothing, a few feet.

Thanks for the help guys.
 