Anybody have any experience/advice concerning a proposed 'voltage
aiding' transformer set up.
Namely a 115 to 230 volt (1:2 step up with completely separate
primary and secondary windings; not an auto transformer).
Input 115 volts with secondary 230 volts 'added' to produce an
output of 345 volts to power three 347 volt commercial
fluorescent light fixtures. Each fixture equipped with two 60
watt 96 inch tubes, a total of six 60 watt tubes plus ballast
transformer inefficiencies and possible power factor.
My figuring says that the transformer will have to up voltage
from 115 to 230 and be capable of handling two thirds of the
total wattage (VA), approximately. Also that it's secondary
winding must be able to carry the total input current since that
will flow through both windings in the 'series voltage aiding'
configuration.
Several primary/secondary transformers available; one, typically
is rated 340 VA, 115 to 230 volts.
Also have an a centre tapped auto transformer 0-115-230 available
but haven't figured out a way to use that in a voltage aiding
situation; at least with a suitable and conventional zero
potential neutral connection to the fixtures, also it would
require 230 volts (which is available) and double pole switching
of that 230 volt input which would like to avoid.
Would anyone like to push a pencil around and recommend ideas or
problems? Any suggestions ranging from "Crazy idea" to practical
considerations welcomed. When weather gets wintry intend to 'test
bench' this idea and possibly build into workshop; I've got scads
of spare 96 inch light tubes, more than we'll ever need, a spare
347 volt ballast; the fixtures were free and will provide 24 feet
of lighting, ideal for our 44 foot long workshop along with other
spot lighting over specific items.
Thanks for any input. Terry.
aiding' transformer set up.
Namely a 115 to 230 volt (1:2 step up with completely separate
primary and secondary windings; not an auto transformer).
Input 115 volts with secondary 230 volts 'added' to produce an
output of 345 volts to power three 347 volt commercial
fluorescent light fixtures. Each fixture equipped with two 60
watt 96 inch tubes, a total of six 60 watt tubes plus ballast
transformer inefficiencies and possible power factor.
My figuring says that the transformer will have to up voltage
from 115 to 230 and be capable of handling two thirds of the
total wattage (VA), approximately. Also that it's secondary
winding must be able to carry the total input current since that
will flow through both windings in the 'series voltage aiding'
configuration.
Several primary/secondary transformers available; one, typically
is rated 340 VA, 115 to 230 volts.
Also have an a centre tapped auto transformer 0-115-230 available
but haven't figured out a way to use that in a voltage aiding
situation; at least with a suitable and conventional zero
potential neutral connection to the fixtures, also it would
require 230 volts (which is available) and double pole switching
of that 230 volt input which would like to avoid.
Would anyone like to push a pencil around and recommend ideas or
problems? Any suggestions ranging from "Crazy idea" to practical
considerations welcomed. When weather gets wintry intend to 'test
bench' this idea and possibly build into workshop; I've got scads
of spare 96 inch light tubes, more than we'll ever need, a spare
347 volt ballast; the fixtures were free and will provide 24 feet
of lighting, ideal for our 44 foot long workshop along with other
spot lighting over specific items.
Thanks for any input. Terry.