UPS or Uninterrupted Power Supplies is an important unit of the AC
Power Conditioning Systems the world over and along with AC Servo
Stabilizers, CVT (Constant Voltage Transformers) or Ferro Resonant
transformer do the conditioning of raw AC power coming from electrical
utilities and supply clean and regulated power to the devices
connected to them..

The raw AC power coming from the Utilities will have noise, break,
black out, brown out , variation in voltage and frequency because of
the load connected to it and also because of transmission effect.
Normally the generating station will be away in a remote area and
transmission lines take the power generated through out the country by
the action called Transmission and distribution (T& D ). The power
generated will be at a higher voltage level of 33KV or 11 KV which
will be then boosted up to 230/400KVA and then transmitted through
power transmission towers and when it reaches the distribution sub
station the voltage is reduced to 11 KV and finally when it comes to
the customer from the road side transformer it will be 230 V AC in
India or 110V AC as in US. This voltage also can be either single
phase or three phase at the preference of the user or customer.

As said the AC voltage will have the problems mentioned above which
can damage sensitive instruments like Refrigerator, Air conditioners,
Computers etc and warrant the use of power conditioning equipments
called UPS, Inverters, Servo voltage Stabilizers etc to get controlled
and clean Power.



UPS Systems

All the previous mentioned equipments only regulate the AC voltage
and does not help you if the input is having noise, burn out and black
outs and power failure. in this case only we have advantage of UPS
which gives continuous power even when power fails at its input and
removes all the electrical noise and continues to energise the
instruments connected to it.

The very basic UPS consists of

* A charger to charge the battery connected to the UPS when AC
mains is available.
* An Inverter to invert the DC voltage of the battery to AC
* A set of batteries depending on the power of the UPS
* A transfer switch to switch over from AC to mains (Inthe case of
interactive UPS and Standby UPS)

There are three basic types of UPS available in the Market. they are

* Standby UPS Systems . The Inverter which supplies the AC voltage
will be switched 'ON' only when mains fail by a static switch from the
mains to inverter and the inverter continues to supply power till the
batteries drain out. The batteries are getting charged when mains is
available. This is a simple systems and cheaper.
* Line Interactive UPS. This type has only one transformer which
charges the batteries and gives output from the inverter always .
But when mains fail the static switch changes from Mains to battery
and the Inverter always gives out power and connected to the load.

Points to be taken care off.

* Select a UPS depending on your load requirements and never
overload it.

* Do not connect loads which do not require an UPS as the power is
precious as when power is absent it gives life support. Load like
printers should not be connected to UPS.

* Select the batteries properly since these batteries support your
load when mains fail. Batteries should be kept clean and proper
maintenance to be carried out.

* Once power fails try to save all the work and be ready to switch
off as the battery will cut off if their threshold voltage is reached.

* keep the UPS in a ventilated area and easily approachable.As it
is a secondary power people keep them at places which is normally not
approachable. I have once seen it being kept in a toilet. At another
time in a canteen where one fellow kept one cup of tea on the top and
while talking with his colleague poured the tea on the UPS and burned
it by shorting.

* Have all the spare parts ready and have the routine maintenance
carried out.

* Use proper power cables for connection.

If you follow the above your UPS and Stabilizers will give long time
support and service.
 
On Sat, 27 Sep 2008 01:52:31 -0700 (PDT), rajan <nloknath@gmail.com>
wrote:

UPS or Uninterrupted Power Supplies is an important unit of the AC
Power Conditioning Systems the world over and along with AC Servo
Stabilizers, CVT (Constant Voltage Transformers) or Ferro Resonant
transformer do the conditioning of raw AC power coming from electrical
utilities and supply clean and regulated power to the devices
connected to them..

The raw AC power coming from the Utilities will have noise, break,
black out, brown out , variation in voltage and frequency because of
the load connected to it and also because of transmission effect.
Normally the generating station will be away in a remote area and
transmission lines take the power generated through out the country by
the action called Transmission and distribution (T& D ). The power
generated will be at a higher voltage level of 33KV or 11 KV which
will be then boosted up to 230/400KVA and then transmitted through
power transmission towers and when it reaches the distribution sub
station the voltage is reduced to 11 KV and finally when it comes to
the customer from the road side transformer it will be 230 V AC in
India or 110V AC as in US. This voltage also can be either single
phase or three phase at the preference of the user or customer.

As said the AC voltage will have the problems mentioned above which
can damage sensitive instruments like Refrigerator, Air conditioners,
Computers etc and warrant the use of power conditioning equipments
called UPS, Inverters, Servo voltage Stabilizers etc to get controlled
and clean Power.



UPS Systems

All the previous mentioned equipments only regulate the AC voltage
and does not help you if the input is having noise, burn out and black
outs and power failure. in this case only we have advantage of UPS
which gives continuous power even when power fails at its input and
removes all the electrical noise and continues to energise the
instruments connected to it.

The very basic UPS consists of

* A charger to charge the battery connected to the UPS when AC
mains is available.
* An Inverter to invert the DC voltage of the battery to AC
* A set of batteries depending on the power of the UPS
* A transfer switch to switch over from AC to mains (Inthe case of
interactive UPS and Standby UPS)

There are three basic types of UPS available in the Market. they are

* Standby UPS Systems . The Inverter which supplies the AC voltage
will be switched 'ON' only when mains fail by a static switch from the
mains to inverter and the inverter continues to supply power till the
batteries drain out. The batteries are getting charged when mains is
available. This is a simple systems and cheaper.
* Line Interactive UPS. This type has only one transformer which
charges the batteries and gives output from the inverter always .
But when mains fail the static switch changes from Mains to battery
and the Inverter always gives out power and connected to the load.
---
And the third type is...?
---

Points to be taken care off.

* Select a UPS depending on your load requirements and never
overload it.

* Do not connect loads which do not require an UPS as the power is
precious as when power is absent it gives life support. Load like
printers should not be connected to UPS.

* Select the batteries properly since these batteries support your
load when mains fail. Batteries should be kept clean and proper
maintenance to be carried out.

* Once power fails try to save all the work and be ready to switch
off as the battery will cut off if their threshold voltage is reached.

* keep the UPS in a ventilated area and easily approachable.As it
is a secondary power people keep them at places which is normally not
approachable. I have once seen it being kept in a toilet. At another
time in a canteen where one fellow kept one cup of tea on the top and
while talking with his colleague poured the tea on the UPS and burned
it by shorting.

* Have all the spare parts ready and have the routine maintenance
carried out.

* Use proper power cables for connection.

If you follow the above your UPS and Stabilizers will give long time
support and service.

JF
 
On Sat, 04 Oct 2008 06:29:45 -0700, rajan wrote:

The third UPS is the 'ON LINE' ups systems in which the Inverter will be
working all the time and the batteries will be charged and the Inverter
energised by the Charger. It is also called double conversion type since
AC is converted to DC to charge battery and the supply the Inverter and
the DC is converted back to AC by the Inverter.

The Charger and Inverter always work and have two separate transformer.

Sorry, I have missed this in the article.
Then there's the original No-Break system:

motor--generator--flywheel--clutch--diesel engine

I once saw an article on such a system with a flywheel weighing 30 tons.
With that much momentum in the system, they didn't need to air-start the
diesel. It must have been outrageously expensive, but it was designed
before high-power semiconductors became available.
 
On Sep 27, 4:23 pm, John Fields <jfie...@austininstruments.com> wrote:
On Sat, 27 Sep 2008 01:52:31 -0700 (PDT), rajan <nlokn...@gmail.com
wrote:



UPS or Uninterrupted Power Supplies is an important unit of the AC
Power Conditioning Systems the world over and along with AC Servo
Stabilizers, CVT (Constant Voltage Transformers) or Ferro Resonant
transformer do the conditioning of raw AC power coming from electrical
utilities and supply clean and regulated power to the devices
connected to them..

The raw AC power coming from the Utilities will have  noise, break,
black out, brown out , variation in voltage and frequency because of
the load connected to it and also because of transmission effect.
Normally the generating station will be away in a remote area and
transmission lines take the power generated through out the country by
the action called Transmission and distribution (T& D ). The power
generated will be at a higher voltage level of 33KV or 11 KV which
will be then boosted up to 230/400KVA and then transmitted through
power transmission towers  and when it reaches the distribution sub
station the voltage is reduced to 11 KV and finally when it  comes to
the customer from the road side transformer it will be 230 V AC in
India or 110V AC as  in US.  This voltage also can be either single
phase or three phase at the preference of the user or customer.

As said  the AC voltage will have the problems mentioned above which
can damage sensitive instruments like Refrigerator, Air conditioners,
Computers etc and warrant the use of power conditioning equipments
called UPS, Inverters, Servo voltage Stabilizers etc to get controlled
and clean Power.

UPS Systems

All the previous  mentioned equipments only regulate the AC voltage
and does not help you if the input is having noise, burn out and black
outs and power failure. in this case only we have advantage of UPS
which gives continuous power even when power fails at its input and
removes all the electrical noise and continues to energise the
instruments connected to it.

The very basic UPS consists of

   * A charger to charge the battery connected to the UPS when AC
mains is available.
   * An Inverter to invert the DC voltage of the battery to AC
   * A set of batteries depending on the power of the UPS
   * A transfer switch to switch over from AC to mains (Inthe case of
interactive UPS and Standby UPS)

There are three basic types of UPS available in the Market. they are

   * Standby UPS Systems . The Inverter which supplies the AC voltage
will be switched 'ON' only when mains fail by a static switch from the
mains to inverter and the inverter continues to supply power till the
batteries drain out. The batteries are getting charged when mains is
available. This is a simple systems and cheaper.
   * Line Interactive UPS.   This type has only one transformer which
charges the batteries and gives output  from the inverter  always .
But when mains fail the static switch changes from Mains to battery
and the Inverter always gives out power and connected to the load.

---
And the third type is...?
---



Points to be taken care off.

   * Select a UPS depending on your load requirements and never
overload it.

   * Do not connect loads which do not require an UPS as the power is
precious as when power is absent it gives life support. Load like
printers should not be connected to UPS.

   * Select the batteries properly since these batteries support your
load when mains fail. Batteries should be kept clean and proper
maintenance to be carried out.

   * Once power fails try to save all the work and be ready to switch
off as the battery will cut off if their threshold voltage is reached.

   * keep the UPS in a ventilated area and easily approachable.As it
is a secondary power people keep them at places which is normally not
approachable. I have once seen it being kept in a toilet. At another
time in a canteen where one fellow kept one cup of tea on the top and
while talking with his colleague poured the tea on the UPS and burned
it by shorting.

   * Have all the spare parts ready and have the routine maintenance
carried out.

   * Use proper power cables for connection.

If you follow the above your UPS and Stabilizers will give long time
support and service.

JF
The third UPS is the 'ON LINE' ups systems in which the Inverter will
be working all the time and the batteries will be charged and the
Inverter energised by the Charger. It is also called double conversion
type since AC is converted to DC to charge battery and the supply the
Inverter and the DC is converted back to AC by the Inverter.

The Charger and Inverter always work and have two separate
transformer.

Sorry, I have missed this in the article.
 