A very common power distribution transformer uses a DELTA wired primary
and a WYE wired secondary (thus including a neutral connection). In the
WYE secondary, you then can get a lower voltage from the hot-to-neutral
connections, or a higher voltage from the hot-to-hot connections. Some
common voltages:
120 volts hot-to-neutral and 208 volts hot-to-hot in US, Canada
230 volts hot-to-neutral and 400 volts hot-to-hot in Europe
277 volts hot-to-neutral and 480 volts hot-to-hot in US
346 volts hot-to-neutral and 600 volts hot-to-hot in Canada
The interesting thing about this is that while the hot-to-neutral lines
provide power in the same 3 phases that the primary windings have, the
hot-to-hot lines are off by 30 degrees. Normally that is no big deal
since 3 phase machines only care about the phases on what is hooked up.
Now here is my question. Suppose I have a 1 phase device hooked up to
just one pair of hot-to-hot lines. Further suppose this is a resistive
load (power factor 1). At the load the phase relationship between the
voltage and current will be 0 degrees. But what about the relationship
between the voltage and current in the two windings that are feeding
this power? Wouldn't they be off by +30 degrees and -30 degrees? So
wouldn't this appear to them to be a partially reactive load? And what
about the current on the primary side. Wouldn't that reflect the phase
difference there, too?
If the above is true, and it would seem to me to be the case (but I am
asking to have that confirmed since there might be some physics that are
involved that I am not aware of), then if one were expecting to have
loads that are routinely out of balance on a 3 phase line, that the best
choice would be to configure the secondary so that the exact voltage one
needs is provided on exactly one winding (whether the secondary is wired
WYE or DELTA)?
In many commercial buildings, power is provided in three phase due to
the higher capacity, at the 120/208 volt level in the US. This is the
right voltage for the lights and most appliances at the hot-to-neutral
lines. Then the hot-to-hot 208 volts is expected to serve the higher
voltage needs like larger 1 phase air conditioners, electric stoves,
and whatever else needs voltage in that range. But doesn't this kind
of setup potentially put an unbalance demand on the 3 phase connection?
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
| (first name) at ipal.net | http://phil.ipal.org/ http://ka9wgn.ham.org/ |
-----------------------------------------------------------------------------
and a WYE wired secondary (thus including a neutral connection). In the
WYE secondary, you then can get a lower voltage from the hot-to-neutral
connections, or a higher voltage from the hot-to-hot connections. Some
common voltages:
120 volts hot-to-neutral and 208 volts hot-to-hot in US, Canada
230 volts hot-to-neutral and 400 volts hot-to-hot in Europe
277 volts hot-to-neutral and 480 volts hot-to-hot in US
346 volts hot-to-neutral and 600 volts hot-to-hot in Canada
The interesting thing about this is that while the hot-to-neutral lines
provide power in the same 3 phases that the primary windings have, the
hot-to-hot lines are off by 30 degrees. Normally that is no big deal
since 3 phase machines only care about the phases on what is hooked up.
Now here is my question. Suppose I have a 1 phase device hooked up to
just one pair of hot-to-hot lines. Further suppose this is a resistive
load (power factor 1). At the load the phase relationship between the
voltage and current will be 0 degrees. But what about the relationship
between the voltage and current in the two windings that are feeding
this power? Wouldn't they be off by +30 degrees and -30 degrees? So
wouldn't this appear to them to be a partially reactive load? And what
about the current on the primary side. Wouldn't that reflect the phase
difference there, too?
If the above is true, and it would seem to me to be the case (but I am
asking to have that confirmed since there might be some physics that are
involved that I am not aware of), then if one were expecting to have
loads that are routinely out of balance on a 3 phase line, that the best
choice would be to configure the secondary so that the exact voltage one
needs is provided on exactly one winding (whether the secondary is wired
WYE or DELTA)?
In many commercial buildings, power is provided in three phase due to
the higher capacity, at the 120/208 volt level in the US. This is the
right voltage for the lights and most appliances at the hot-to-neutral
lines. Then the hot-to-hot 208 volts is expected to serve the higher
voltage needs like larger 1 phase air conditioners, electric stoves,
and whatever else needs voltage in that range. But doesn't this kind
of setup potentially put an unbalance demand on the 3 phase connection?
--
-----------------------------------------------------------------------------
| Phil Howard KA9WGN | http://linuxhomepage.com/ http://ham.org/ |
| (first name) at ipal.net | http://phil.ipal.org/ http://ka9wgn.ham.org/ |
-----------------------------------------------------------------------------