C
Chris Jones
Guest
Hi all,
If you like the idea of being able to install your own 12 Volt solar
module to run a ventillation fan in your shed, or keep a battery charged
to run a light in your shed, or install any other small solar panels on
your premises, then you might find that it is much harder and more
expensive than it used to be, unless you have your say NOW (by 28th Oct).
The standard for solar installations, AS5033, is being revised, but the
draft standard is open to comments from the public until the 28th.
AS5033 requires such things as:
corrosion resistant mountings, surge protection, uv resistant materials,
circuit breakers, disconnecting devices, earth fault interrupters, steel
wire armoured cables, earthing and bonding arrangements, equipment
marking, wiring identification, fire emergency information,
labelling/signs for disconnection devices, documentation, maintenance
recommendations, commissioning tests, commissioning sheet, insulation
resistance measurement, open circuit voltage measurements, infrared
scan, earth fault protection test, lightning protection, screening and
shielding, etc. etc.
In the future, if you want to know which of these you would need to
apply to your DIY installation you would need to spend a few hundred $$$
buying the standard, then who knows how much more making your little
solar panel comply with complicated rules.
Presently (in the 2012 version of the standard), solar arrays of less
than 240 Watts and less than 50 Volts are outside the scope of the
standard - which is sensible as such modules are not especially
hazardous. The draft standard will remove this restriction for fixed
modules, and only allows PORTABLE arrays to be exempt. So your solar
powered pocket calculator will not need lightning protection and danger
signs, but your solar powered illuminated street number might.
If you would like to have your say on this topic, go to this web address
and find AS5033 and leave some comments:
https://sapc.standards.org.au/sapc/public/listOpenCommentingPublication.action
Here are more instructions for leaving comments:
http://www.standards.org.au/HubTraining/Other/Register%20to%20submit%20a%20comment%20on%20a%20Draft%20Standard.pdf
You need to create an account to read the draft standard and make
comments, but it is free of charge and your only way to influence these
rules.
Chris
If you like the idea of being able to install your own 12 Volt solar
module to run a ventillation fan in your shed, or keep a battery charged
to run a light in your shed, or install any other small solar panels on
your premises, then you might find that it is much harder and more
expensive than it used to be, unless you have your say NOW (by 28th Oct).
The standard for solar installations, AS5033, is being revised, but the
draft standard is open to comments from the public until the 28th.
AS5033 requires such things as:
corrosion resistant mountings, surge protection, uv resistant materials,
circuit breakers, disconnecting devices, earth fault interrupters, steel
wire armoured cables, earthing and bonding arrangements, equipment
marking, wiring identification, fire emergency information,
labelling/signs for disconnection devices, documentation, maintenance
recommendations, commissioning tests, commissioning sheet, insulation
resistance measurement, open circuit voltage measurements, infrared
scan, earth fault protection test, lightning protection, screening and
shielding, etc. etc.
In the future, if you want to know which of these you would need to
apply to your DIY installation you would need to spend a few hundred $$$
buying the standard, then who knows how much more making your little
solar panel comply with complicated rules.
Presently (in the 2012 version of the standard), solar arrays of less
than 240 Watts and less than 50 Volts are outside the scope of the
standard - which is sensible as such modules are not especially
hazardous. The draft standard will remove this restriction for fixed
modules, and only allows PORTABLE arrays to be exempt. So your solar
powered pocket calculator will not need lightning protection and danger
signs, but your solar powered illuminated street number might.
If you would like to have your say on this topic, go to this web address
and find AS5033 and leave some comments:
https://sapc.standards.org.au/sapc/public/listOpenCommentingPublication.action
Here are more instructions for leaving comments:
http://www.standards.org.au/HubTraining/Other/Register%20to%20submit%20a%20comment%20on%20a%20Draft%20Standard.pdf
You need to create an account to read the draft standard and make
comments, but it is free of charge and your only way to influence these
rules.
Chris