I need to determine if this UPS can be modified to tolerate minor swings in
line frequency (as from a generator) without switching to and staying on
battery power.
We have a situation where the power goes out, the generator comes on, but
the UPS continues to stay on battery with 'input power fault' displayed on
its panel. Occasionally, the generator, under load, drops to 60hz and the
UPS will switch to line power until the loads that have slowed it slightly
have been removed. It runs at 62 hz with only a couple of kilowatts of load.
I think that the generator is spec'd at 60hz when at half to 2/3 load, which
is a lot more than our continuous load.
At any rate, a schematic for this 1992-vintage UPS would help me determine
if the frequency sensing circuit can be modified to increase its tolerance.
Right now, if the line isn't exactly 60.0hz, it will switch to battery power
and stay there.
Does anyone have any ideas about modifying this particular (1200RM) UPS for
the above requirements?
Another option is to spend $1200 on a new APC SmartUPS, with no garantee
that it will tolerate generator power (although we do have an APC SmartUPS
650 VA in another office that seems perfectly happy with the 62hz generator
frequency). I'd like to avoid that gamble, if I can modify this unit with
the help of documentation.
The recent power blackout necessitated bypassing the big UPS and running a
network 'barefoot' off the generator output, a practice I do not like.
--
Take care,
Mark & Mary Ann Weiss
VIDEO PRODUCTION . FILM SCANNING . AUDIO RESTORATION
Hear my Kurzweil Creations at: http://www.dv-clips.com/theater.htm
Business sites at:
www.dv-clips.com
www.mwcomms.com
www.adventuresinanimemusic.com
-
line frequency (as from a generator) without switching to and staying on
battery power.
We have a situation where the power goes out, the generator comes on, but
the UPS continues to stay on battery with 'input power fault' displayed on
its panel. Occasionally, the generator, under load, drops to 60hz and the
UPS will switch to line power until the loads that have slowed it slightly
have been removed. It runs at 62 hz with only a couple of kilowatts of load.
I think that the generator is spec'd at 60hz when at half to 2/3 load, which
is a lot more than our continuous load.
At any rate, a schematic for this 1992-vintage UPS would help me determine
if the frequency sensing circuit can be modified to increase its tolerance.
Right now, if the line isn't exactly 60.0hz, it will switch to battery power
and stay there.
Does anyone have any ideas about modifying this particular (1200RM) UPS for
the above requirements?
Another option is to spend $1200 on a new APC SmartUPS, with no garantee
that it will tolerate generator power (although we do have an APC SmartUPS
650 VA in another office that seems perfectly happy with the 62hz generator
frequency). I'd like to avoid that gamble, if I can modify this unit with
the help of documentation.
The recent power blackout necessitated bypassing the big UPS and running a
network 'barefoot' off the generator output, a practice I do not like.
--