I have a simple question regarding shielded cable. I take it for granted
that the proper way to ground a cable shield is at the end where the power
source is. I assume this is true. I understand why it is wrong to ground at
both ends but I can't explain why it is proper to ground at the end nearest
the power source. I have learned from experience that grounding at the end
away from the power source can cause interference.
In my particular application I have a single 12VDC proximity sensor mounted
on a rock crusher. All other electrical components on the crusher and other
equipment in the plant are 120VAC or 460VAC 3ph. Electrical power around
portable rock crushing plants is typically provided by a generator set and
various parts of the plant are connected via a maze of cables lying on the
ground or strung through conveyor supports. It is an inherently electrically
noisy environment.
I have a 12VDC power source mounted in a remotely mounted push button
control enclosure which is tied by a multiconductor cable to another
enclosure where the 120VAC control power enters the control assembly. The
pushbutton control enclosure is grounded via a grounding conductor in the
cable to the chassis ground that comes in with the control power. The
proximity sensor on the crusher is connected to the push button enclosure
via a shielded cable. This sounds more complicated than it is.
My question is: Is it proper to ground the shield at the push button
enclosure (and hence via the grounding conductor to the control power
ground)? If so why exactly? It seems intuitively obvious but I can't really
explain why.
Jon Juhlin
that the proper way to ground a cable shield is at the end where the power
source is. I assume this is true. I understand why it is wrong to ground at
both ends but I can't explain why it is proper to ground at the end nearest
the power source. I have learned from experience that grounding at the end
away from the power source can cause interference.
In my particular application I have a single 12VDC proximity sensor mounted
on a rock crusher. All other electrical components on the crusher and other
equipment in the plant are 120VAC or 460VAC 3ph. Electrical power around
portable rock crushing plants is typically provided by a generator set and
various parts of the plant are connected via a maze of cables lying on the
ground or strung through conveyor supports. It is an inherently electrically
noisy environment.
I have a 12VDC power source mounted in a remotely mounted push button
control enclosure which is tied by a multiconductor cable to another
enclosure where the 120VAC control power enters the control assembly. The
pushbutton control enclosure is grounded via a grounding conductor in the
cable to the chassis ground that comes in with the control power. The
proximity sensor on the crusher is connected to the push button enclosure
via a shielded cable. This sounds more complicated than it is.
My question is: Is it proper to ground the shield at the push button
enclosure (and hence via the grounding conductor to the control power
ground)? If so why exactly? It seems intuitively obvious but I can't really
explain why.
Jon Juhlin