Several weeks ago I posted a query here about the advisability and/or
precautions to take in paralleling batteries for a UPS, (an APC Smart
UPS-700 Net). It normally takes one pair of 12v 7AH batteries, from
which I was getting ~5-7 minutes of run time with a 65% load (as
reported by APC Powerchute Biz Edition 7.119).
Jerry G, Roni L. and Kris S. warned that the recharge might not be
sufficient and to check float voltages with and w/o batteries
paralleled, to use batteries of comparable vintage, and to be sure extra
long run time didn't cause overheating.
I built an appropriate 12 Gauge cable and used the Run Time calibration
feature of the APC software. 4 batteries gave me no more run time than
pair A or pair B alone. I carefully rechecked connections, made sure no
connector was running hot and end up w. the same results. 4 batteries
give me the same run time as either pair. Total float current is about
12.5ma, 5ma on pair B, 7.5 on pair A).
I'm stumped. I've set things up so that I just pull off or stick back
on just one spade lug every time I do the test. What is going on?
I should be getting at least 2x the run time, (more since the slower
the consumption the more AH the battery yields.)
Any suggestions more than welcome.
precautions to take in paralleling batteries for a UPS, (an APC Smart
UPS-700 Net). It normally takes one pair of 12v 7AH batteries, from
which I was getting ~5-7 minutes of run time with a 65% load (as
reported by APC Powerchute Biz Edition 7.119).
Jerry G, Roni L. and Kris S. warned that the recharge might not be
sufficient and to check float voltages with and w/o batteries
paralleled, to use batteries of comparable vintage, and to be sure extra
long run time didn't cause overheating.
I built an appropriate 12 Gauge cable and used the Run Time calibration
feature of the APC software. 4 batteries gave me no more run time than
pair A or pair B alone. I carefully rechecked connections, made sure no
connector was running hot and end up w. the same results. 4 batteries
give me the same run time as either pair. Total float current is about
12.5ma, 5ma on pair B, 7.5 on pair A).
I'm stumped. I've set things up so that I just pull off or stick back
on just one spade lug every time I do the test. What is going on?
I should be getting at least 2x the run time, (more since the slower
the consumption the more AH the battery yields.)
Any suggestions more than welcome.