On Sunday, August 11, 2019 at 2:10:45 AM UTC-4, upsid...@downunder.com wrote:
Interesting. Can you provide a resource that talks about this? When exactly was this event? I'm surprised the grid can "ask" a generator to supply any given amount of power. I thought an inverter connected supplier would just provide what it can and that's all. Inverters are normally designed to track the frequency and voltage of the grid. I'm not sure how the grid would "ask" the supplier to provide more power.
--
Rick C.
++-+ Get 1,000 miles of free Supercharging
++-+ Tesla referral code - https://ts.la/richard11209
On Sat, 10 Aug 2019 17:17:09 -0700 (PDT), Bill Sloman
bill.sloman@ieee.org> wrote:
On Sunday, August 11, 2019 at 2:03:40 AM UTC+10, upsid...@downunder.com wrote:
On Sat, 10 Aug 2019 13:52:03 +0100, Martin Brown
'''newspam'''@nezumi.demon.co.uk> wrote:
[1] There blackouts across the Midlands, the South East,
South West, North West and north east of England, and
Wales.
It seems likely that the initial problem which was the first gas turbine
generator dropping out wasn't dealt with in the two minutes before a
second independent failure of a wind turbine farm. The two being offline
together then took the mains frequency sufficiently far out of bounds
that some inverters stopped as well. Cascade failure followed.
It also may be that they had a bit bad luck.
Good network management requires that the N-1 rule is followed. The
network should survive the loss of _largest_ production unit. In
practice during the first minutes the spinning reserve of other power
plants are used (.i.e. overloading them). During that time quick
start emergency gas turbines are started, which then takes over from
the spinning reserve. When the emergency gas turbines are running, the
power of existing power plants are added e.g. by burning more coal to
get more steam or other slower starting power plants are starting.
When these are running, the emergency gas turbines can be shut down
and the N-1 criterion is restored, waiting for the loss of the next
largest production unit. These emergency gas turbines are typically
running for less than an hour.
However, as long as the emergency gas turbines are used, the network
doesn't tolerate the loss of the next largest unit.
When South Australia bought its big Telsa battery, with the fast inverter built in, it more or less immediately demonstrated the convience of having a really fast-acting voltage and frequency correcting device.
https://reneweconomy.com.au/how-the-tesla-big-battery-kept-the-lights-on-in-south-australia-20393/
Dinowig is fast, but not that fast.
snip
Originally the idea with the N-1 rule was that after the failure of
the largest production unit, the remaining production units can be
slightly overloaded for a while until new production capacity has ben
dispatched (spinning reserve).
This assumption is true with _BIG_ synchronous generators with can be
overloaded by 5 - 10 % for a minute or two without overheating too
much. Thus if a 1000 MW unit is lost the total grid on-line capacity
needs to be 10-20 GW, each of which can be overloaded by 5 - 10 %,
After this minute or two, fast starting emergency gas turbines or
diesels must be running so that the big generators can be scaled down
to nominal capacity.
However, a lot of renewable sources are inverter connected. These
inverters have no overload capacity or at most a few second capability
before overheating.
About a decade ago there was a huge wind energy boom in Germany due to
ample subsidies, so that every farmer wanted a wind turbine on their
field, no matter how bad the wind conditions are. These could also
sell all production to the net, this running at 100 % load as long as
there is wind.
In a fault condition. when all remaining production were asked to
provide the spinning reserve, i.e overloading of generators. Since
many wind turbines had practically no overload capability, some were
tripped more or less immediately before the emergency gas turbines had
been started. With loss of some wind turbine production the remaining
capacity was asked to produce more overload power. More and more wind
turbines overloaded and tripped. The wind turbine tripping rippled
through the network.
Interesting. Can you provide a resource that talks about this? When exactly was this event? I'm surprised the grid can "ask" a generator to supply any given amount of power. I thought an inverter connected supplier would just provide what it can and that's all. Inverters are normally designed to track the frequency and voltage of the grid. I'm not sure how the grid would "ask" the supplier to provide more power.
--