C
Chris Carlen
Guest
Hi:
Look at page 40 in this document on their powder cores:
http://www.mag-inc.com/pdf/2004_Magnetics_Powder_Core_Catalog.zip
The wire diameters and areas are way off from what you'd calculate using
the AWG formula:
d = 0.005*92^((36-AWG)/39) [in]
I thought maybe they were insulated diameters, from their use of the
term "heavy build".
But if that was the case, then the areas would still be right according
to the AWG formula. But they are too large as well.
For instance 22ga wire should be:
d = 0.02535 in = 0.6438 mm
A = 642.4 circ mils = 0.3255 mm^2
But Magnetics lists:
d = 0.701 mm
A = 810 circ mils = 0.411 mm^2
Notice, their area doesn't match the diameter, which would lead to 0.386
mm^2.
What are they doing?
Interestingly, their current capacities are close to, but still a bit in
error from the values one would calculate based on the correct areas
(the copper, not the insulated wire).
Good day!
--
_______________________________________________________________________
Christopher R. Carlen
Principal Laser/Optical Technologist
Sandia National Laboratories CA USA
crcarle@sandia.gov -- NOTE: Remove "BOGUS" from email address to reply.
Look at page 40 in this document on their powder cores:
http://www.mag-inc.com/pdf/2004_Magnetics_Powder_Core_Catalog.zip
The wire diameters and areas are way off from what you'd calculate using
the AWG formula:
d = 0.005*92^((36-AWG)/39) [in]
I thought maybe they were insulated diameters, from their use of the
term "heavy build".
But if that was the case, then the areas would still be right according
to the AWG formula. But they are too large as well.
For instance 22ga wire should be:
d = 0.02535 in = 0.6438 mm
A = 642.4 circ mils = 0.3255 mm^2
But Magnetics lists:
d = 0.701 mm
A = 810 circ mils = 0.411 mm^2
Notice, their area doesn't match the diameter, which would lead to 0.386
mm^2.
What are they doing?
Interestingly, their current capacities are close to, but still a bit in
error from the values one would calculate based on the correct areas
(the copper, not the insulated wire).
Good day!
--
_______________________________________________________________________
Christopher R. Carlen
Principal Laser/Optical Technologist
Sandia National Laboratories CA USA
crcarle@sandia.gov -- NOTE: Remove "BOGUS" from email address to reply.