I'm wanting to set up a transformer to deliver 50% of its' power by
applying a tap at the 7th turn of a 14 turn secondary. There are two in the
circuit but, only one will be modified. The only data I have on the
transformers is from my own calculations: (ignoring losses)
Power: .7kVA (each) Pri.: 120 turns Sec.: 14 turns Ratio:
116
The formula I used to get I is:
Isec = Ipri x Tpri /
Tsec
Using this formula, I get 14 volts @ 49.97 amps. Again, using this same
formula for the tap, I get 7 volts @ 99.94 amps. Something has to be
wrong with my approach. I'm tapping for less but, according to this, I'm
getting more. What did I miss or, am I thinking in reverse?