Isolation transformer?

B

Bob Engelhardt

Guest
I was looking for a 120-120 isolation transformer on eBay and I kept
finding 120-240/480 transformers. There are 2 secondaries on these
(connect in parallel or series). It occurred to me that I could use one
of these as a 120-120 by using one secondary as input and the other
secondary as output. I know that this is theoretically possible, but
are there practical reasons why it wouldn't work?

Also: if one of these 120-240/480 transformers is rated 500VA, that
means 1 amp on the secondary, right? I.e., 1A at 480v.

Thanks,
Bob
 
On Sun, 28 Jul 2019 19:56:47 -0400, Bob Engelhardt
<BobEngelhardt@comcast.net> wrote:

I was looking for a 120-120 isolation transformer on eBay and I kept
finding 120-240/480 transformers. There are 2 secondaries on these
(connect in parallel or series). It occurred to me that I could use one
of these as a 120-120 by using one secondary as input and the other
secondary as output. I know that this is theoretically possible, but
are there practical reasons why it wouldn't work?

Also: if one of these 120-240/480 transformers is rated 500VA, that
means 1 amp on the secondary, right? I.e., 1A at 480v.

Thanks,
Bob

You can use a 120/240-to-anything transformer as a 120-120 isolation
tranny. Connect one half of the official primary to the line and use
the other half as the isolated output. Ignore the "secondary". The
power rating will be a bit less than specified because you're not
using all the copper.


--

John Larkin Highland Technology, Inc

lunatic fringe electronics
 
On 2019-07-28, Bob Engelhardt <BobEngelhardt@comcast.net> wrote:
I was looking for a 120-120 isolation transformer on eBay and I kept
finding 120-240/480 transformers. There are 2 secondaries on these
(connect in parallel or series). It occurred to me that I could use one
of these as a 120-120 by using one secondary as input and the other
secondary as output. I know that this is theoretically possible, but
are there practical reasons why it wouldn't work?

Also: if one of these 120-240/480 transformers is rated 500VA, that
means 1 amp on the secondary, right? I.e., 1A at 480v.

Thanks,
Bob

it depends how much isolation you need, using two secondaries, or
two primaries as halves of an isolation transformer only gets you
functional insulation, not any kind of safety isolation.

if the output is grounded and the input is fused, that may be enough.

--
When I tried casting out nines I made a hash of it.
 
On Sun, 28 Jul 2019 19:56:47 -0400, Bob Engelhardt
<BobEngelhardt@comcast.net> wrote:

I was looking for a 120-120 isolation transformer on eBay and I kept
finding 120-240/480 transformers. There are 2 secondaries on these
(connect in parallel or series). It occurred to me that I could use one
of these as a 120-120 by using one secondary as input and the other
secondary as output. I know that this is theoretically possible, but
are there practical reasons why it wouldn't work?

Also: if one of these 120-240/480 transformers is rated 500VA, that
means 1 amp on the secondary, right? I.e., 1A at 480v.

Thanks,
Bob

You can, that is the intent on providing the duel windings.
 
John Larkin wrote:

You can use a 120/240-to-anything transformer as a 120-120 isolation
tranny. Connect one half of the official primary to the line and use
the other half as the isolated output.

** The secondary voltage available under load will be lower than the input - depending on the regulation of the particular unit.


Ignore the "secondary". The
power rating will be a bit less than specified because you're not
using all the copper.

** Actually it will be higher for the same reason.

With rated current in both halves of the primary, having no secondary current means the unit will run cooler - allowing up to 41% increase in primary current.

AC supply transformers are tricky things.


.... Phil
 
default wrote:
You can, that is the intent on providing the duel windings.

** I guess those "duel" winding get to really fight it out ?



.... Phil
 
Bob Engelhardt wrote:
I was looking for a 120-120 isolation transformer on eBay and I kept
finding 120-240/480 transformers. There are 2 secondaries on these
(connect in parallel or series). It occurred to me that I could use one
of these as a 120-120 by using one secondary as input and the other
secondary as output. I know that this is theoretically possible, but
are there practical reasons why it wouldn't work?

** A 120-120 transformer does not have equal windings, the secondary has additional turns to allow for the regulation factor of the unit. Might be anywhere from 4 to 20% extra turns on the output side.

Also, a properly made 120-120 would also have good insulation between the two windings rather than them being overlaid or wound bifilar.

Another factor is magnetising current - transformer primaries are sized to allow for the extra current but secondaries are not since there is none.



Also: if one of these 120-240/480 transformers is rated 500VA, that
means 1 amp on the secondary, right? I.e., 1A at 480v.

** Yep - the VA rating describes what rms current x voltage available from the secondary.


..... Phil
 
On Mon, 29 Jul 2019 05:11:41 -0700 (PDT), Phil Allison
<pallison49@gmail.com> wrote:

default wrote:


You can, that is the intent on providing the duel windings.



** I guess those "duel" winding get to really fight it out ?
You are right, I screwed up, and it wasn't so you could show how petty
and insecure you really are.
 
default = another idiot troll wrote:

default wrote:


You can, that is the intent on providing the duel windings.



** I guess those "duel" winding get to really fight it out ?

You are right, I screwed up, and it wasn't so you could show how petty
and insecure you really are.

** No sense of humour = typical ASD fucked troll.


..... Phil
 
On Sunday, July 28, 2019 at 6:57:45 PM UTC-5, Bob Engelhardt wrote:
I was looking for a 120-120 isolation transformer on eBay and I kept
finding 120-240/480 transformers. There are 2 secondaries on these
(connect in parallel or series). It occurred to me that I could use one
of these as a 120-120 by using one secondary as input and the other
secondary as output. I know that this is theoretically possible, but
are there practical reasons why it wouldn't work?

Also: if one of these 120-240/480 transformers is rated 500VA, that
means 1 amp on the secondary, right? I.e., 1A at 480v.

Thanks,
Bob

I have one you can have for free. You just have to pay postage.

It weighs in at 9 lbs.

Bando Shielded Power Transformer Yamaha BD21A35E-0004
 
On Monday, July 29, 2019 at 8:03:42 PM UTC-5, AK wrote:
On Sunday, July 28, 2019 at 6:57:45 PM UTC-5, Bob Engelhardt wrote:
I was looking for a 120-120 isolation transformer on eBay and I kept
finding 120-240/480 transformers. There are 2 secondaries on these
(connect in parallel or series). It occurred to me that I could use one
of these as a 120-120 by using one secondary as input and the other
secondary as output. I know that this is theoretically possible, but
are there practical reasons why it wouldn't work?

Also: if one of these 120-240/480 transformers is rated 500VA, that
means 1 amp on the secondary, right? I.e., 1A at 480v.

Thanks,
Bob

I have one you can have for free. You just have to pay postage.

It weighs in at 9 lbs.

Bando Shielded Power Transformer Yamaha BD21A35E-0004

I forgot this.

This came from a Yamaha 240 watt receiver.
 
On 7/29/2019 9:03 PM, AK wrote:
I have one you can have for free. You just have to pay postage.

It weighs in at 9 lbs.

Bando Shielded Power Transformer Yamaha BD21A35E-0004

Thanks, but my need for one has gone away.
 
On 7/29/2019 8:09 AM, Phil Allison wrote:
** A 120-120 transformer does not have equal windings, the secondary has additional turns to allow for the regulation factor of the unit. Might be anywhere from 4 to 20% extra turns on the output side.

Also, a properly made 120-120 would also have good insulation between the two windings rather than them being overlaid or wound bifilar.

Another factor is magnetising current - transformer primaries are sized to allow for the extra current but secondaries are not since there is none.

....

Thanks - I had overlooked that. It might not have mattered (lower
output might have been OK), but I'm not going to use one now.
 
Thanks for the replies; I've decided not to use a transformer.
 
Bob Engelhardt wrote:
Phil Allison wrote:
** A 120-120 transformer does not have equal windings, the secondary has additional turns to allow for the regulation factor of the unit. Might be anywhere from 4 to 20% extra turns on the output side.

Also, a properly made 120-120 would also have good insulation between the two windings rather than them being overlaid or wound bifilar.

Another factor is magnetising current - transformer primaries are sized to allow for the extra current but secondaries are not since there is none..

...

Thanks - I had overlooked that. It might not have mattered (lower
output might have been OK), but I'm not going to use one now.

** Funny how we get the same question here regularly - and the same answers..

Larkin posts his usual naĂŻve bullshit and I correct him with the real facts.

He has commented, more than once, that he treats usenet posting as a big joke.

What he doe not realise is how that makes him look like a big joke.



..... Phil
 
On Mon, 29 Jul 2019 17:06:39 -0700 (PDT), Phil Allison
<pallison49@gmail.com> wrote:

default = another idiot troll wrote:


default wrote:


You can, that is the intent on providing the duel windings.



** I guess those "duel" winding get to really fight it out ?

You are right, I screwed up, and it wasn't so you could show how petty
and insecure you really are.



** No sense of humour = typical ASD fucked troll.


.... Phil
If you think your rudeness is somehow humorous, you don't know the
definition of humor. But perhaps you'd like to double-down, dig
yourself in deeper and explain...
 
default is another boring autistic pig wrote:



You can, that is the intent on providing the duel windings.



** I guess those "duel" winding get to really fight it out ?

You are right, I screwed up, and it wasn't so you could show how petty
and insecure you really are.



** No sense of humour = typical ASD fucked troll.


.... Phil

If you think your rudeness is somehow humorous, you don't know the
definition of humor. But perhaps you'd like to double-down, dig
yourself in deeper and explain...

** Sorry, no can do - my tiny joke needs no explanation.

Get yourself some counselling on your place on the autism spectrum.

It might help, a bit.

Suicide is also an option.

Nobody alive would miss you.



..... Phil
 
On Tue, 30 Jul 2019 05:22:33 -0700 (PDT), Phil Allison
<pallison49@gmail.com> wrote:

default is another boring autistic pig wrote:





You can, that is the intent on providing the duel windings.



** I guess those "duel" winding get to really fight it out ?

You are right, I screwed up, and it wasn't so you could show how petty
and insecure you really are.



** No sense of humour = typical ASD fucked troll.


.... Phil

If you think your rudeness is somehow humorous, you don't know the
definition of humor. But perhaps you'd like to double-down, dig
yourself in deeper and explain...


** Sorry, no can do - my tiny joke needs no explanation.

Get yourself some counselling on your place on the autism spectrum.

It might help, a bit.

Suicide is also an option.

Nobody alive would miss you.



.... Phil
Few things are more pathetic than a bully who lacks the power to
intimidate. Few things are funnier than a bully who lacks the power
to intimidate but fails to understand their limitations - thanks for
the laughs.
 
On Monday, 29 July 2019 03:47:49 UTC+1, John Larkin wrote:
On Sun, 28 Jul 2019 19:56:47 -0400, Bob Engelhardt
BobEngelhardt@comcast.net> wrote:

I was looking for a 120-120 isolation transformer on eBay and I kept
finding 120-240/480 transformers. There are 2 secondaries on these
(connect in parallel or series). It occurred to me that I could use one
of these as a 120-120 by using one secondary as input and the other
secondary as output. I know that this is theoretically possible, but
are there practical reasons why it wouldn't work?

Also: if one of these 120-240/480 transformers is rated 500VA, that
means 1 amp on the secondary, right? I.e., 1A at 480v.

Thanks,
Bob

You can use a 120/240-to-anything transformer as a 120-120 isolation
tranny. Connect one half of the official primary to the line and use
the other half as the isolated output. Ignore the "secondary". The
power rating will be a bit less than specified because you're not
using all the copper.

Sort of. Vout will be a little low under load due to copper resistance. That could be solved by putting eg a 12v secondary in series with the output, connected right way round. But the big issue is that you won't have a level of isolation that's considered safe for many applications. For some jobs it's adequate, for many not.


NT
 
Not mine. It is built from a very high power amp, around 1,000 watts per channel. The secondary at 120 puts out 127, when I load the shit out of it and it drops to 120 the line voltage drops to like 116.

I had to scrap it, the amp boards got soaked with the elements and got conductive, and the protection didn't even work and it had offset and was blowing speakers.

It came out of a bar in the ceiling and I think the roof leaked on it but they didn't own the brick and mortar so they didn't give a shit.

Anyway, the load that made it drop you 120, a 1,500 watt electric heater. I don't even want to think what one with that capacity would cost. I go it for free. I didn't charge any fee just kept it, which they were cool with.
 