I need help (KVA) again (incorrect addition on previous post

G

george

Guest
Hi,

I would like to know the Kva for the following appliances.

4 freezers at 5 amps each

3 chiller units at 3 amps each

2 chillers at 35 amps each.

I do not know if they are resistive or conductive(if that is necessary
for the answer)

Would the answer be 99 * 240 /1000 = 23.76??

Hope you can help.

Confused
 
"John Fields" <jfields@austininstruments.com> wrote in message
news:gbbb51pm40sg0pbqtenpv88dv8kesg840a@4ax.com...
On 7 Apr 2005 14:43:43 -0700, george_holland222@hotmail.com (george)
wrote:

Hi,

I would like to know the Kva for the following appliances.

4 freezers at 5 amps each

3 chiller units at 3 amps each

2 chillers at 35 amps each.

I do not know if they are resistive or conductive(if that is necessary
for the answer)

Would the answer be 99 * 240 /1000 = 23.76??

Hope you can help.

---
It's not "conductive", it's "reactive", but if you're taking the
ratings from the nameplates and you're running the appliances on 240V
mains then, yes, it's 23.76 kVA,

--
John Fields
Professional Circuit Designer
Notice that John write kVA as opposed to your Kva...John is right so write
the units that way.
 
---
It's not "conductive", it's "reactive", but if you're taking the
ratings from the nameplates and you're running the appliances on 240V
mains then, yes, it's 23.76 kVA,

--
John Fields
Professional Circuit Designer

Notice that John write kVA as opposed to your Kva...John is right so write
the units that way.
Thanks for your help. You see, I have a shop and I am having a new
supply of electricity and I have beeen asked for kVA(now I know the
answer I can take it a stage further and contact an electrician to do
the necessary work)

George
 