Is earth of 25 ohms at 60 hz and some amps also 25 ohms at
thousands of amps? Of course not. Resistance is only linear
within certain limits. No resistance remains linear -
constant - once we apply extreme voltages or currents. One
important parameter that defines a complete breakdown of
linear resistance is called breakdown voltage. The NEC only
defines continuity of earth within the current and frequency
ranges used by utilities.
Measure the resistance across a fluorescent tube. A 25 watt
tube must be on the order of 2000 ohms to conduct sufficient
AC electric currents. So why is that resistance in excess of
10 megohms? Again, resistance in earth and in that
fluorescent tube, is not constant for all electrical
parameters.
10 centimeters of air has multi-megohms of resistance. Many
kilometers of megohm resistors in series clearly means that
lightning cannot pass through air. And yet those many megohm
resistors become an excellent conductor of 2kamp or 20 kamp
lightning currents. How can this be? As megohms of air
become a good conductor, then so does 25 ohms of earth become
an even better conductor.
Lightning could travel 5 kilometers diagonally over to
earthborne charges - to complete an electric circuit. But a
shorter electrical path is 3 kilometers of air down to earth
and 4 kilometers through earth because, during the current
transient, earth become far more conductive than '25 ohms'.
This even though 300,000 multi-megohm resistors in air become
perfectly good conductors.
I never avoided that 25 ohms. A responsible person never
asked about those 25 ohms. When that earth resistance at 60
hz and a few amps becomes less, then that same soil becomes
even more conductive during a CG lightning strike. 25 ohms
verses other soils is a good indication as to how conductive
soil may be also during strike. But earth is not at 25 ohms
when conducting the most common 2 Kamp or 10 Kamp lightning
strikes. Earth, like air, becomes extremely conductive which
is why lighting seeks earth ground and which is why good earth
grounds make lightning rods and 'whole house' protectors so
effective.
Rather than criticize, please cite specific reference where
citation was misrepresented. Lem Instruments was only
provided as a reference on how earth conductivity is measured
- in the electrical domain defined by NEC. It was not cited
to sell anything. In the meantime NEC does not even define
how that 25 ohms should be measured. Earthing system does not
measure 25 ohms during the CG strike just like air does not
maintain multi-megohms of resistance.
Joe Van wrote:
Well actually the references do seem a bit .... shall we say
Careless but then like all the references w_tom comes up with
it is trying to sell something. On the whole though it does not
appear too bad - on a cursory flick through it there are no
glaring errors.
Of course it does point out a small fact that w_tom keeps carefully
avoiding and that is that the resistance to earth for a single
earth stake is considered by the NEC is less than 25 Ohms -
calculate the EPR on that of a Lightning strike of say a
conservative 10,000 Amps.
...