I need some real-world perspective, please.
There's a big power transformer in a power amp I'm working on. The amp is
supposed to produce 1000W RMS (though we all know how amp specs are...).
The fuse at the input is 10A for 120V mains, and the label says 1100VA. So
the transformer is somewhere around 1kVA.
Now, when I hook this transformer up to 120V, with no load connected, it
hums loudly and it draws 1.1A from the line.
Interestingly, the current (remember, no load connected) is only about 0.5A
at 105V, and there is almost no hum. The hum and the current go up very
steeply as I increase the voltage to 120V, using a variac.
The secondary voltages measure what I'd expect: 138VAC rms across the outer
taps, 31VAC rms across the inner taps. DC resistance, subtracting the
resistance of shorted probes, is 0R37 across the outer taps, 0R58 across the
inner taps, and 0R38 across the primaries (in 120V mode, which has the two
primary windings in parallel).
Does this seem right? Has this transformer gotten toasted somehow, or is
this normal? I've never seen that much no-load current draw or hum, but I
don't usually work with amps this powerful, either.
Thanks!
There's a big power transformer in a power amp I'm working on. The amp is
supposed to produce 1000W RMS (though we all know how amp specs are...).
The fuse at the input is 10A for 120V mains, and the label says 1100VA. So
the transformer is somewhere around 1kVA.
Now, when I hook this transformer up to 120V, with no load connected, it
hums loudly and it draws 1.1A from the line.
Interestingly, the current (remember, no load connected) is only about 0.5A
at 105V, and there is almost no hum. The hum and the current go up very
steeply as I increase the voltage to 120V, using a variac.
The secondary voltages measure what I'd expect: 138VAC rms across the outer
taps, 31VAC rms across the inner taps. DC resistance, subtracting the
resistance of shorted probes, is 0R37 across the outer taps, 0R58 across the
inner taps, and 0R38 across the primaries (in 120V mode, which has the two
primary windings in parallel).
Does this seem right? Has this transformer gotten toasted somehow, or is
this normal? I've never seen that much no-load current draw or hum, but I
don't usually work with amps this powerful, either.
Thanks!