I've looked thgrough the NEC code book but have been unable to find my
answer there. I'm sure it's there someplace but I can't find it.
Anyway, in my wife's new shop she needs another sink installed. The
ideal wall has a Load Center (breaker panel) already installed. The
bottom of the panel is 60 inches from the floor. The sink height will
be 30 inches from the floor. The sink will be almost directly beneath
the panel so there will be 20 inches from the sink to the panel. Will
the proposed location be a code violation?
Thanks,
Eric
 
etpm@whidbey.com wrote:
Greetings All,
I've looked thgrough the NEC code book but have been unable to find my
answer there. I'm sure it's there someplace but I can't find it.
Anyway, in my wife's new shop she needs another sink installed. The
ideal wall has a Load Center (breaker panel) already installed. The
bottom of the panel is 60 inches from the floor. The sink height will
be 30 inches from the floor. The sink will be almost directly beneath
the panel so there will be 20 inches from the sink to the panel. Will
the proposed location be a code violation?

Talk to the local building inspector, since they have the final say.


--
http://improve-usenet.org/index.html

aioe.org, Goggle Groups, and Web TV users must request to be white
listed, or I will not see your messages.

If you have broadband, your ISP may have a NNTP news server included in
your account: http://www.usenettools.net/ISP.htm


There are two kinds of people on this earth:
The crazy, and the insane.
The first sign of insanity is denying that you're crazy.
 
etpm@ whidbey.com wrote:
This group is about stuff with transistors or toobs.

The folks most familiar the minutiae of the NEC
are in alt.engineering.electrical.
 
<etpm@whidbey.com> wrote in message
news:4957e526.68885191@news.whidbey.net...
Greetings All,
I've looked thgrough the NEC code book but have been unable to find my
answer there. I'm sure it's there someplace but I can't find it.
Anyway, in my wife's new shop she needs another sink installed. The
ideal wall has a Load Center (breaker panel) already installed. The
bottom of the panel is 60 inches from the floor. The sink height will
be 30 inches from the floor. The sink will be almost directly beneath
the panel so there will be 20 inches from the sink to the panel. Will
the proposed location be a code violation?
Thanks,
Eric
Check the clearance regs around the panel box. You can't block access.
 
On Mon, 29 Dec 2008 07:35:50 -0500, "Tom Biasi"
<tombiasi@optonline.net> wrote:

etpm@whidbey.com> wrote in message
news:4957e526.68885191@news.whidbey.net...
Greetings All,
I've looked thgrough the NEC code book but have been unable to find my
answer there. I'm sure it's there someplace but I can't find it.
Anyway, in my wife's new shop she needs another sink installed. The
ideal wall has a Load Center (breaker panel) already installed. The
bottom of the panel is 60 inches from the floor. The sink height will
be 30 inches from the floor. The sink will be almost directly beneath
the panel so there will be 20 inches from the sink to the panel. Will
the proposed location be a code violation?
Thanks,
Eric

Check the clearance regs around the panel box. You can't block access.


Thanks Tom and everyone else who replied. Your answer Tom is the one
that fit. I finally was able to get an inspector to call back when I
was available, eliminating ongoing phone tag. In Washington all
electrical inspections are done by the state through Labor and
Industries so it's hard sometimes to actually speak to an inspector.
As it turns out blocking access is the problem. No permanent
structures, like a counter or sink, are allowed beneath or above the
panel and 30 inches to each side. So I will need to put the sink on
another wall.
Cheers,
Eric
 